[Bldg-sim] Daylight saving simulation in eQUEST
Eleanor Lee
eslee at lbl.gov
Fri Jun 20 10:02:34 PDT 2008
The numbers seem reasonable but there are a few ways you can check:
1. If you're using DOE-2/ Equest, check the depth of your zone &
photosensor location against head height of window. Rule of thumb is
daylit depth is ~1.5 times head height of window so typical zone depth
for 9-ft ceiling is about 15 ft with sensor at 2/3rds or 10 ft distance
from window. DOE-2 has limitations in calc with split-flux method:
internally reflected component is overestimated for distances greater
than approx 2 times head height of window which can lead to
overestimation of lighting energy use savings. Also, pay attention to
interior shading schedule/ modeling assumptions. If you have a bare
window, you're going to get great savings but uncomfortable occupants.
2. Check results against some other software packages:
DAYSIM or Daylight123 via Christoph Reinhardt, which uses Radiance as
core engine but friendly user interface
Run your facade design through http://commglazing.datrona.com/facade.php
in about 5 minutes (database based on DOE-2)
Run SPOT tool (Radiance with GUI)
Compare switching strategies vs dimming strategies (ballast energy
consumption differs between strategies), include occupancy-sensors in
model for base & test cases
3. Field data:
New York Times Headquarters monitored data for open plan office with
actively managed shades:
http://gaia.lbl.gov/btech/papers/56979.pdf
30-48% avg annual lighitng energy savings for west facing windows and
75% for bilaterally daylit SW facing windows
with dimming, setpoint tuning, nighttime occupancy (no occ sensors
during daytime since open plan).
Owner informally reports an operating avg LPD of 0.35 W/ft2 for May/June
08 with installed LPD of 1.0 W/ft2.
http://windows.lbl.gov/comm_perf/newyorktimes.htm
HMG, NREL, Weidt Group reports savings that are significantly less than
predicted savings depending on attention paid to proper execution
(reports published on 0-10V systems) & in particular for sidelighting
applications. DALI-enabled digital lighting controls (used at NYT) is
making it easier to achieve more reliable results but still not a slam
dunk yet.
Hope this helps,
el.
On 6/20/2008 6:19 AM, Lan Hu wrote:
> Hi, all,
>
> I simulated an office building with 49% window on each orientation, and
> compared the results with daylighting and without daylight. The lighting
> energy consumption is 48.5% less with daylighting, and the total energy
> consumption is 18.5% less. I set the only sensor in each exterior zone
> around 15ft from the exterior window and used default values for other
> setup. I wonder if anybody with experience of daylighting think these
> big(?) saving numbers are realistic?
>
> Any input will be appreciated.
>
> Lan Hu
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
More information about the Bldg-sim
mailing list