[Bldg-sim] LEED and Title-24 and E-Quest and ASHRAE-90.1
Eric Shadd
EShadd at archenergy.com
Mon Mar 17 12:42:25 PDT 2008
You can check the .CAL file to find _some_ information on why the building didn't pass T24. Check for spaces that are outside the throttling range in the SIM files. Verify that your constructions in the compliance section are from the Joint Appendices.
Also, if you brought the model into eQuest by opening the INP and making a new eQuest PD2 file, verify that the weather file is correct.
-Eric
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080317/bcb2ceb0/attachment-0002.htm>
More information about the Bldg-sim
mailing list