[Bldg-sim] TMY3 Released with 1020 US Locations
Horowitz, Scott
Scott_Horowitz at nrel.gov
Thu May 15 08:30:17 PDT 2008
The DOE2 documentation is a little confusing in this regard. Here are
the general steps:
1. Copy your TMY2 file to DOE2's EXENT directory and rename to
WEATHR.TMP
2. Create a file called INPUT.TMP in the EXENT directory
3. In the INPUT.TMP file, put the following text. Be sure to replace the
city, state, and station number as appropriate for your location. You
can find this information in the first line of the TMY2 file.
PACK
PHOENIX AZ TMY2
TMY2 23183
STAT
END
4. Run the DOEWTH.EXE executable (it will automatically use the
WEATHR.TMP and INPUT.TMP files above as inputs). This will create a
NEWTH.TMP file in the EXENT directory that is your bin weather file for
use with DOE2. Just rename to Location.bin and you're set.
Scott
--
Scott Horowitz
Center for Buildings & Thermal Systems
National Renewable Energy Laboratory
1617 Cole Blvd.
Golden, CO 80401
303.384.7560
> -----Original Message-----
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-
> bounces at lists.onebuilding.org] On Behalf Of Tim Johnson
> Sent: Wednesday, May 14, 2008 1:29 PM
> To: Randy Wilkinson; bldg-sim at onebuilding.org
> Subject: Re: [Bldg-sim] TMY3 Released with 1020 US Locations
>
> I am attempting to follow these steps, but I can't seem to figure out
how
> to use the DOE2 unilities. It looks like it is only DOS based and I
am
> not familiar with DOS. Could you walk me through the steps to convert
> from .TM2 to .bin using the DOE2 utility?
> Thanks,
> Tim
>
> >>> Randy Wilkinson <randy at hvacware.net> 05/14/08 11:21 AM >>>
> Be aware that what NREL calls TMY2 weather data is true text based
TMY2
> weather data per their original definition. DOE2 (eQuest) uses a
binary
> version of the TMY2 weather files. The binary version is about 1/10th
> the file size of the original text based TMY2 file. You need to use
> another weather processor to convert the true TMY2 into a binary
version
> (xxxxxx.BIN) for use with eQuest. You can't just rename the file as
it
> sounds like you did.
>
> step 1 - Get the TMY3 weather file for your location
> step 2 - Use NREL's TMY3toTMY2 converter to convert it to TMY2
> step 3 - Use DOE2 or EnergyPlus weather utilities to convert the text
> based TMY2 weather file to a binary version for use with DOE2 (eQuest)
>
> I think you skipped step 3.
>
> Randy Wilkinson
>
> James Hess wrote:
> > Great news on the TMY3 weather data. We want to start using it in
> eQuest.
> >
> > However, FYI... in order to test the new TMY3 files out, we
downloaded a
> TMY3
> > weather file for Little Rock, AR. Then we converted the TMY3 file
to
> TMY2
> > (using same name as TMY2 --> LITTLEAR.BIN ), placed it in a new
folder
> under
> > eQuest weather (Weather\TMY3) then tried to use in eQuest and got an
> error,
> > and the simulation would not run.
> >
> > Is there any additional information that we need to know in order to
> make
> > this work?
> >
> >
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
BLDG-SIM-
> UNSUBSCRIBE at ONEBUILDING.ORG
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
BLDG-SIM-
> UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Bldg-sim
mailing list