[Bldg-sim] Space Cooling Energy Consumption with GSHP
Adam Young
way at freese.com
Wed May 14 06:57:42 PDT 2008
Good morning,
I am having similar results with a ground-coupled heat pump and am
following this thread closely. I am only realizing savings of about 5%
to 10% over an air-source HP.
I believe I am incorrectly separating out the fan-energy on the
air-source units. What is the procedure for getting the fan and
compressor energy separate on the air-source units (12 SEER air-source
unit per 90.1-2004, baseline design)? If I understand correctly, the
GCHP efficiency stated under ARI 13256 does not include external fan
energy or external pump energy, and therefore, the stated GCHP
efficiency can be converted into EIR directly. Correct?
Also, for the GCHP the correct number to use is the "GLHP EER" value
from the manufacturer based on ARI 13256, which is higher than the
water-loop HP (WLHP) ARI EER? Is that correct?
Experience tells me a GCHP should realize more savings than what I am
getting, which leads me to believe I am inputting "garbage" into the
model. Thanks for your help!
Adam Young
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Demba
Ndiaye
Sent: Wednesday, May 14, 2008 8:05 AM
To: Tom Butler; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Space Cooling Energy Consumption with GSHP
Thomas,
You should definitively have more savings than that, even if there is
the pump energy.
One first thing to check: the efficiency of GSHP should be much higher
than that of air-source heat pumps in both heating and cooling modes.
______________
Demba Ndiaye
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Tom Butler
Sent: Tuesday, May 13, 2008 5:53 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Space Cooling Energy Consumption with GSHP
I am modeling an apartment style dormitory for a project in Atlanta, GA.
Each of the 45 units is served by its own heat pump, along with a few
zones for public areas. For an energy efficiency grant application I
have compared the designed system, a ground source heat pump, with an
air source heat pump prescribed by 90.1. Other than the systems, the
models are identical.
The energy use for space cooling is significantly higher for the GSHP
system (24,000 kWh vs. 17,000 kWh). Because the power required to run
pumps offsets the savings in heating energy, this destroys the rationale
for spending the extra money on the Ground Source Heat Pump, as well as
our chances of receiving the grant.
Has any one encountered this issue?
Thanks
tb
Thomas Butler, LEED AP
Direct Phone 404-253-1435 | Direct Fax 404-253-1335
LORD, AECK & SARGENT ARCHITECTURE
Responsive Design * Technological Expertise * Exceptional Service
www.lordaecksargent.com <file:///\\www.lordaecksargent.com>
_ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _ _
This electronic mail message is intended exclusively for the individual or
entity to which it is addressed. This message, together with any attachment,
may contain the sender's organization's confidential and privileged information.
The recipient is hereby notified to treat the information as
confidential and privileged and to not disclose or use the information except
as authorized by sender's organization. Any unauthorized review, printing,
retention, copying, disclosure, distribution, retransmission, dissemination
or other use of, or taking of any action in reliance upon, this information
by persons or entities other than the intended recipient is prohibited.
If you received this message in error, please immediately contact the sender
by reply email and delete all copies of the material from any computer.
Thank you for your cooperation.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080514/44e5bc4c/attachment-0002.htm>
More information about the Bldg-sim
mailing list