[Bldg-sim] Plant Process Loads
Seth P. Spangler
sspangle at rmf.com
Tue May 20 06:15:41 PDT 2008
LEED 2.2 v.1 Reference Manual, Page 182 under the Process Energy Header.
"Process energy cost shall be equal to at
least 25% of the Baseline Building Performance."
ASHRAE 90.1-2004 App G, Table G3.1 Section 12.
Receptacle and other Loads
Receptacle and process loads, such as those for office and other
equipment, shall be estimated based on the building type or space
type category and shall be assumed to be identical in the proposed
and baseline building designs, except as specifically authorized by
the rating authority. These loads shall be included in simulations of
the building and shall be included when calculating the baseline
building performance and proposed building performance.
Please correct me if I am misinterpreting something.
Thanks.
Seth Spangler, LEED(r) AP
Design Engineer
RMF Engineering, Inc
Ph: (843) 971-9639 ext:108
Fax: (843) 971-9641
sspangle at rmf.com
________________________________
From: James V. Dirkes II P.E. [mailto:jvd2pe at tds.net]
Sent: Tuesday, May 20, 2008 8:51 AM
To: Seth P. Spangler
Subject: RE: [Bldg-sim] Plant Process Loads
Dear Seth,
What makes you think that process loads must be a minimum of 25%? As I
understand process load, there's often NO such load in a building... and
I did not think that there was any requirement to model it if it did not
exist.
Got a paragraph number in 90.1 which refers to that? (I cannot find
one.)
The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Seth P.
Spangler
Sent: Tuesday, May 20, 2008 8:04 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Plant Process Loads
Hello All,
I am in the planning stage of modeling a campus boiler plant. I have two
questions as follows:
1) ASHRAE/LEED require a minimum process energy of 25% of the
total building energy. I am predicting that my plant (15 boilers plus
pumps etc.) process load will be 95% of my buildings energy use if not
more. Is there a way to reduce the process energy use of the plant for
energy modeling purposes other than an exceptional calculation method?
2) Is this a situation where I could perform an exceptional
calculation and compare a "standard" boiler plant to the high efficiency
one that is being installed?
Thanks in advance for your help.
Seth Spangler, LEED(r) AP
Design Engineer
RMF Engineering, Inc
Ph: (843) 971-9639 ext:108
Fax: (843) 971-9641
sspangle at rmf.com