[Bldg-sim] eQuest - FCU - how to make it cycle
Yuvaraj Saravanan
Yuvaraj.Saravanan at arup.com
Wed Sep 24 14:07:11 PDT 2008
Mark,
I don't disagree with you. You may be right. But is there any
documentation which says it is how equest reports the supply air
flow-rate?
Other thing is, I am having a continously operating exhasut fan and
outside air fan (24/7) and intermittently operating FCU. Attached is the
hourly report. In this case I have a 100 cfm exhaust and outside air. If
you are right then I dont understand how the ratio of OSA/supply air
flow-rate is reported. Can you give me your insights?
Regards,
Yuvaraj
-----Original Message-----
From: Mark Prince [mailto:mprince at aeieng.com]
Sent: Wednesday, September 24, 2008 11:15 AM
To: Yuvaraj Saravanan; bldg-sim at lists.onebuilding.org;
equest-users-bounces at lists.onebuilding.org
Subject: Re: [Bldg-sim] eQuest - FCU - how to make it cycle
Yuvaraj,
I believe the "intermittent" mode is the correct way to model this.
When you look at the hourly reports it appears that the fan coil is
varying the airflow rate. However, I believe eQuest is calculating the
percentage of the hour that the FCU operates and then calculates an
average airflow during that entire hour. Say the FCU has a constant
volume airflow capacity of 500 CFM, but during one hour it only cycles
on for a third of the hour. I believe eQuest would then report this
airflow as 166 CFM for that hour in the hourly report.
Hope this helps.
If you disagree please let me know.
Sincerely,
Mark Prince
Affiliated Engineers
5802 Research Park Blvd.
Madison, WI 53719
(608) 441-6668
mprince at aeieng.com
>>> "Yuvaraj Saravanan" <Yuvaraj.Saravanan at arup.com> 9/24/2008 12:56 PM
>>> >>>
Hi All,
Does anyone know how to make a FCU cycle ON/OFF based on the zone
thermostat setting? I tried choosing the "Fan on mode" to be
intermittent in the Fan->Flow parameters tab. When I make the fan to be
intermittent, fan is cycling but the supply CFM is no more a constant
volume. It is varying the supply CFM. I observed this in the hourly
report.
ASHRAE standard 90.1 requires the fan to cycle to meet the loads during
unoccupied hours. How everybody model this in eQuest when you have a FCU
system?
Any suggestions is greatly appreciated.
Regards,
Yuvaraj
> ______________________________________________
Yuvaraj Saravanan, PE
Engineer
> Arup
12777 West Jefferson Boulevard Suite 200 Los Angeles CA 90066
> tel: 1 310 578 4400
dir: 1 310 578 4521
> fax: 1 310 577 7011
internal freecall: x20521
yuvaraj.saravanan at arup.com
> www.arup.com
>
>
____________________________________________________________
Electronic mail messages entering and leaving Arup business systems are
scanned for acceptability of content and viruses
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Project 9 - Baseline Design - Hourly Results 5.csv
Type: application/octet-stream
Size: 421222 bytes
Desc: Project 9 - Baseline Design - Hourly Results 5.csv
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080924/d790320f/attachment-0001.obj>
More information about the Bldg-sim
mailing list