[Bldg-sim] Quearies
sambhav tiwari
tiwari.sambhav at gmail.com
Thu Nov 12 02:49:45 PST 2009
Dear Sir,
I have some doubts in ASHRAE90.1 statements as follows
Page 178 G.3.1.3.11
1 Heat rejection: "Condenser water design supply temperature shall be
85F or 10F approach at design wet bulb temperature,whichever is lower,
with a design temperature rise of 10F". I could not understand meaning
of this statement can anyone through light on this statement.
2: G 3.1.3.10
Chilled water pumps: "Chilled water pumps in system less than
120000ft2 shall be modeled as a primary/secondary systems with
secondary pump riding the pump cure" Can anyone explain the meaning of
this statement.
Thanks
Sambhav Tiwari
More information about the Bldg-sim
mailing list