[Bldg-sim] Baseline Modeling for LEED
Christopher Schaffner
chris at greenengineer.com
Fri Nov 20 08:31:47 PST 2009
Under current LEED EAc1/ASHRAE 90.1: Use the same ventilation rate in both
base and design cases, with a few limited exceptions (read the CIRs about
lab air change rates, etc.)
This will likely evolve for LEED 2012.
Chris Schaffner, PE
Vice-Chair EA TAG
On 11/19/09 5:19 PM, "Vikram Sami" <VSami at lasarchitect.com> wrote:
> I always assumed that if you went to 30% extra, you kept the baseline at 100%,
> and the designed building at 130%, but after reading this, it does seem to
> make sense that you would increase both occurrences.
>
> Can anyone from the EA Tag chime in?
>
>
> Vikram Sami, LEED AP
> Direct Phone 404-253-1466 | Direct Fax 404-253-1366
> LORD, AECK & SARGENT ARCHITECTURE
>
>
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nathan Miller
> Sent: Thursday, November 19, 2009 4:42 PM
> To: 'Rimes, Christie'; 'Steven Rutter'; bldg-sim at lists.onebuilding.org
> Subject: Re: [Bldg-sim] Baseline Modeling for LEED
>
> I disagree, I believe the models should be same-same on ventilation rates. See
> section 90.1 (2004) Section G3.1.2.5. It states:
>
> ³Minimum outdoor air ventilation rates should be the same for the proposed and
> baseline building designs.²
>
> In my projects (including those that include 30% additional outside air), I
> have always used the same outdoor air flow rates, unless I was taking credit
> for demand control ventilation in the proposed case (see the exception allowed
> in that same ASHRAE section).
>
>
> Nathan Miller
> Senior Energy Engineer/Mechanical Engineer
> direct: 206.788.4577
> fax: 206.285.7111
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rimes, Christie
> Sent: Thursday, November 19, 2009 1:32 PM
> To: Steven Rutter; bldg-sim at lists.onebuilding.org
> Subject: Re: [Bldg-sim] Baseline Modeling for LEED
>
> In my experience you do not increase the baseline energy model as you are
> being awarded (gaining that point) when you achieve the ventilation credit.
> There are a few similar situations in LEED where by achieving one credit will
> prevent you from achieving another but this happens to everyone so it works
> out to be somewhat fair.
>
>
>
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Steven Rutter
> Sent: Thursday, November 19, 2009 1:25 PM
> To: bldg-sim at lists.onebuilding.org
> Subject: [Bldg-sim] Baseline Modeling for LEED
>
> All,
> There is a credit in LEED (EQc2.0) that involves increasing the required
> ventilation rate by 30%. In trying to achieve this credit, the amount of
> energy would have to increase to condition that additional 30% OSA. Does
> anyone know if you are supposed to increase the baseline energy model¹s
> ventilation rate so it has the same ventilation rate as the proposed building?
> Thank you in advance for your help.
>
>
> Steven Rutter, LEED® AP, EIT
>
>
> 3850 Happy Lane|Sacramento, CA 95827
> O:916-368-0336|F:916-368-0337|C:916-717-7484
> P Please consider the environment before printing this email.
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091120/b927c06b/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 10665 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091120/b927c06b/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2306 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091120/b927c06b/attachment-0001.jpeg>
More information about the Bldg-sim
mailing list