[Bldg-sim] District Thermal Energy - LEED v3
Andrew Craig
AndrewC at InterfaceEng.Com
Fri Apr 2 15:39:18 PDT 2010
Yuvaraj---
This is addressed directly in the LEED Reference Guide for Green
Building Design and Construction, 2009 Edition. Starting on page 267
they go through various central plant scenarios and how they should be
treated. For a district CHP, they reference the same "Required
Treatment of District Thermal Energy, May 2008" that you mention below.
I don't see it clearly addressed, but it seems that you should replace
any reference to 90.1-2004 to 90.1-2007 for a LEED 2009 project if
that's what you used to develop the baseline. Might be worth a CIR
though? Good luck.
Regards,
Andrew Craig EIT, LEED AP
Mechanical Designer / Energy Analyst
INTERFACE ENGINEERING
email andrewc at interfaceeng.com <mailto:andrewc at interfaceeng.com>
direct 503.382.2696
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Yuvaraj
Saravanan
Sent: Friday, April 02, 2010 3:21 PM
To: bldg-sim at lists.onebuilding.org; equest-users at lists.onebuilding.org
Subject: [Bldg-sim] District Thermal Energy - LEED v3
I am trying to do energy model for 3 buildings in a campus. Each
building is seeking separate LEED certification. We have a new central
plant with Ice storage which will serve all three buildings. I have a
USGBC guideline "Required Treatment of District Thermal Energy
in LEED-NC version 2.2 and LEED for Schools" dated May 28, 2008, which
discusses about how to carry out the energy modeling. I am wondering is
there a similar document for LEED version 3. If there is no such
document released by USGBC for version 3, then if I follow the
aforementioned document, the problem I have is, it reference everything
back to ASHRAE 90.1-2004 but LEED V3 follows 90.1-2007. Can anyone guide
me how to approach this situation?
Thanks,
Yuvaraj
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100402/52d9fb7b/attachment-0002.htm>
More information about the Bldg-sim
mailing list