[Bldg-sim] DOAU in Baseline vs. Proposed Model
Chris Jones
cj at enersave.ca
Fri Apr 23 07:19:12 PDT 2010
Its an interesting problem because if the DAOU is
a system has over 5000 cfm and over 70% OA the
baseline system requires heat recovery
(G3.1.2.10). I know because I asked the question
of ASHRAE as an Interpretation Request. Even
though the individual systems served by the DAOU
have less than 70% OA, the baseline systems still
require heat recovery of at least 50% effectiveness.
At 11:53 AM 4/22/2010, Carol Gardner wrote:
>In my opinion, it should not be modeled in the
>baseline building and outdoor air should be added to the systems.
>Carol
>
>On Thu, Apr 22, 2010 at 8:11 AM, Seth P.
>Spangler <<mailto:sspangle at rmf.com>sspangle at rmf.com> wrote:
>
>Hello All,
>
>
>
>For the majority of the LEED projects I work on
>I decouple the space load from the ventilation
>load by using a dedicated outdoor air unit
>(DAOU). Before GBCI took over the review process
>the proposed and baseline models contained the
>same number of systems meaning if we used a DOAU
>in the proposed model - we modeled the same
>unit in the baseline. I recently received a
>comment to remove the DOAU from the baseline and
>add the ventilation air to the space load
>systems. For that particular model it didnt
>have a very big impact so I didnt think twice about it.
>
>
>
>The question should a DOAU be modeled in the
>baseline case or should the outdoor air load be
>added to the mechanical systems that take care of the space load?
>
>
>
>Thanks
>
>
>
>Seth Spangler, LEED® AP
>
>Project Engineer
>
>
>
>RMF Engineering, Inc
>
>Ph: (843) 971-9639 ext:1497
>
>Fax: (843) 971-9641
>
><mailto:sspangle at rmf.com>sspangle at rmf.com
>
>_______________________________________________
>Bldg-sim mailing list
><http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a
>blank message to
><mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a
>blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
Chris Jones
14 Oneida Avenue
Toronto, ON M5J 2E3.
Tel. 416-203-7465
Fax. 416-946-1005
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100423/65063639/attachment-0002.htm>
More information about the Bldg-sim
mailing list