[Bldg-sim] Occupancy

Peter Simmonds peter.simmonds at ibece.net
Wed Dec 8 13:01:46 PST 2010


This is a very important point that is often forgotten in simulation
modeling. The computer is a strange object and if you tell the computer
to put one occupant for every 100ft2, then is does just that and the
related ventilation air and cooling (or heating).

I usually request the architect provide me with the occupation
calculations for the elevators and cafeteria and also the Fire Marshall
rating for building occupancy. These numbers are typically around 70% of
the simulation program occupants. The occupancy density in the program
and therefore be adjusted to match this.

How this could be interpreted in 90.1 I will leave up to any following
discussions?

 

Peter Simmonds, Ph.D. 
Senior Associate
Head of the Advanced Technology Group
IBE Consulting Engineers
14130 Riverside Drive, Suite 201
Sherman Oaks, CA 91423 
p: (818) 377-8220 x246 m: (818) 219-1284 f: (818) 377-8230

www.ibece.com <http://www.ibece.com/> 
Ideas for the built environment

This e-mail message, including any attachments, is for the sole use of
the intended recipient(s) and may contain confidential and privileged
information. Any unauthorized review, use, disclosure, or distribution
is prohibited. If you are not the intended recipient, please contact the
sender by reply e-mail and destroy all copies of the original message.

From: Brian Tysoe [mailto:BTysoe at mcw.com] 
Sent: Wednesday, December 08, 2010 6:50 AM
To: 'bldg-sim at lists.onebuilding.org'
Subject: [Bldg-sim] Occupancy

 

Hello all,

 

I have a question about occupancy schedules for energy models.

 

Generally the owner will provide peak occupancy numbers on a
room-by-room basis; and a peak overall occupancy number for the entire
building. Inevitably the room-by-room numbers will add up to
significantly more than the overall building number.

 

Which numbers should be used for the energy model? Would you use the
room-by-room number and scale them down with the occupancy schedule
based on the overall occupancy?

 

Obviously, this has a significant impact on the results.

 

Thanks,

 

 

Brian Tysoe M.A.Sc., P.Eng., LEED AP 

Mechanical Engineer 

 

MCW Consultants Ltd. <http://www.mcw.com> 

600-156 Front Street West 
Toronto, ON M5J 2L6 
Phone 416-598-2920 
Fax 416-598-5394 

 

This e-mail may be privileged and confidential. Any unauthorized use is
strictly prohibited. If you received this e-mail in error, please
contact the sender directly. 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101208/adbcd648/attachment-0001.htm>


More information about the Bldg-sim mailing list