In regard to exterior surface solar reflectance, ASHRAE 90.1 focuses only on
roofs and not walls. In the 90.1-2007 version, Table 5.5.3.1 has U-Factor
requirements for high albedo roofs (formerly referred to as "cool roofs".)
This single table is a replacement for the roof U-Factor requirements found
in Tables 5.5-1 through 5.5-3 (i.e., climate zones 1 through 3.) The
definition of "high albedo" is found earlier in Section 5.5.3.1.1 as roofs
with a minimum Solar Reflective Index (SRI) of 0.82. Typically, this is a
roof of high emissivity as well as high reflectance. The 90.1 User's Manual
shows values that achieve an SRI of 0.82 in Table 5-D, ranging from an
(e=0.75, refl=0.7) to (e=0.1, refl=0.81) combinations.
Regards,
LOD
===========================
Larry O. Degelman, P.E.
Professor Emeritus of Architecture
Texas A&M University
===========================
--------------------------------------------------
From: "sambhav tiwari" <tiwari.sambhav at gmail.com>
Sent: Tuesday, January 12, 2010 11:31 PM
To: <bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Queary
> Hi,
> I had a query whether ASHRAE 90.1 mentions what value has to
> be taken for wall and roof absorptance as it mentions for U value . As
> absorptance value has great impact on heat gains and further on energy
> consumption.
>
> Can we have a better wall absorptance in proposed case from base case
> so to improve energy performance
>
> Any response will be highly appreciable.
>
> Thanks
> Sambhav Tiwari.
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Bldg-sim
mailing list