I am wondering how EnergyPlus handles the effect
of saturated soil in insulation value; especially
in winter when the damp/wet soil would be
frozen. I am interested mostly in heating loads.
At 07:26 PM 6/26/2010, Drury B Crawley wrote:
> From the EnergyPlus Input-Output Reference, the
> fields describing the green roof top layer include:
>Height of Plants {m}
>Leaf Area Index {dimensionless}
>Leaf Reflectivity {dimensionless}
>Leaf Emissivity
>Minimum Stomatal Resistance (s/m)
>
>(this is on page 183 of the IORef PDF (page
>number
>144):
><http://apps1.eere.energy.gov/buildings/energyplus/pdfs/inputoutputreference.pdf>http://apps1.eere.energy.gov/buildings/energyplus/pdfs/inputoutputreference.pdf)
>
>
>The Engineering Reference describes the
>equations beginning on page 114 of the PDF (page number 90):
><http://apps1.eere.energy.gov/buildings/energyplus/pdfs/engineeringreference.pdf>http://apps1.eere.energy.gov/buildings/energyplus/pdfs/engineeringreference.pdf
>
>
>
>On Fri, Jun 25, 2010 at 10:41 AM, Nick Caton
><<mailto:ncaton at smithboucher.com>ncaton at smithboucher.com> wrote:
>
>
>Open question:
>
>
>
>Ive ascribed to the tack an R / thermal mass
>value onto a new layer approach in the past
>but would appreciate a more nuanced approach if
>it could be done quickly enough.
>
>
>
>Im curious: Does EnergyPlus or any other
>option/model out there account the variable
>shading effects of the foliage on the roof
>construction, as a user might define it? Ive
>speculated this element could be handled
>relatively simply in eQuest using a
>geometrically adjacent shading surface with an
>annual fractional schedule, but eQuest (to my
>experience) doesnt have a clean approach to
>account for the varying thermal mass and
>insulative properties of soil that varies in moisture over time
>
>
>
>~Nick
>
>
>
>
>
>NICK CATON, E.I.T.
>
>PROJECT ENGINEER
>
>25501 west valley parkway
>
>olathe ks 66061
>
>direct 913 344.0036
>
>fax 913 345.0617
>
>Check out our new web-site @
><http://www.smithboucher.com/>www.smithboucher.com
>
>
>
>From:
><mailto:bldg-sim-bounces at lists.onebuilding.org>bldg-sim-bounces at lists.onebuilding.org
>[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Drury B Crawley
>Sent: Friday, June 25, 2010 9:25 AM
>To: <mailto:bldg-sim at lists.onebuilding.org>bldg-sim at lists.onebuilding.org
>Subject: [Bldg-sim] Modeling a Green Roof
>
>
>
>EnergyPlus has a model for green roofs built in
>-- based on experimental measurements and
>experience of researchers at Portland State
>University, Prof David
>Sailor: <http://web.cecs.pdx.edu/~sailor/>http://web.cecs.pdx.edu/~sailor/
>
>
>
>
>---------- Forwarded message ----------
>From: Jeremy Poling
><<mailto:jpoling at epsteinglobal.com>jpoling at epsteinglobal.com>
>Date: Fri, Jun 25, 2010 at 10:04 AM
>Subject: Re: [Bldg-sim] Modeling a Green Roof
>To:
><mailto:Jason.Boehning at ricegardner.com>Jason.Boehning at ricegardner.com,
><mailto:bldg-sim at lists.onebuilding.org>bldg-sim at lists.onebuilding.org
>
>
>
>Penn State University
>(<http://horticulture.psu.edu/cms/greenroofcenter/>http://horticulture.psu.edu/cms/greenroofcenter/)
>and Michigan State University
>(<http://www.hrt.msu.edu/greenroof/>http://www.hrt.msu.edu/greenroof/)
>both have significant research programs on green
>roofs. I would recommend looking at the results
>of the Penn State study on energy transfer in
>Green Roofs
>(<http://etda.libraries.psu.edu/theses/approved/WorldWideFiles/ETD-4616/Thesis_Paulo_Tabares_revised.pdf>http://etda.libraries.psu.edu/theses/approved/WorldWideFiles/ETD-4616/Thesis_Paulo_Tabares_revised.pdf).
>In general, green roofs handle energy through
>the insulating effects of soil, the cooling
>effects of evapotranspiration in the plants, and
>water flows within the green roof
>assembly. This means that a calculated R-value
>will be different depending on the amount of
>plant material participating in
>evapotranspiration, the wetness of the soil, and
>whether the roof is intensive or extensive. A
>straight R-value approach is very simplified and
>should be used with the understanding that model
>results are much less likely to be
>accurate. The Penn State study gives a review
>of published literature showing extensive green
>roofs have R-values between 1.8 and 4.8 while
>intensive green roofs have R-values between 5 and 20.
>
>
>
>In general, the average R-value of soil is 0.25
>per inch, so for a 12 soil depth the R-value of
>the soil would be R-3 excluding assumptions on
>soil wetness and evapotranspiration. We
>typically go conservative and just model the
>R-value of the additional soil since you would
>need a TRNSYS or MatLab model to take into
>account the other energy benefits of a green roof.
>
>
>
>JEREMY R. POLING, PE, LEED AP
>Associate Vice President,
>
>Senior Sustainability Analyst
>Strategic Services
>Site Solutions | Operations | Sustainability
>
>EPSTEIN
>
>Epstein is a firm believer in sustainability. We
>ask that you please consider the environment before printing this e-mail.
>
>
>
>From:
><mailto:bldg-sim-bounces at lists.onebuilding.org>bldg-sim-bounces at lists.onebuilding.org
>[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Fareed Syed
>Sent: Friday, June 25, 2010 8:05 AM
>To: Jason Boehning;
><mailto:bldg-sim at lists.onebuilding.org>bldg-sim at lists.onebuilding.org
>Subject: Re: [Bldg-sim] Modeling a Green Roof
>
>
>
>I heard from our director of sustainability to
>use R-5 for a typical green roof. It was confirmed by few senior architects.
>
>
>
>Thanks,
>
>
>
>Fareed
>
>
>
>From:
><mailto:bldg-sim-bounces at lists.onebuilding.org>bldg-sim-bounces at lists.onebuilding.org
>[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jason Boehning
>Sent: Friday, June 25, 2010 8:46 AM
>To: <mailto:bldg-sim at lists.onebuilding.org>bldg-sim at lists.onebuilding.org
>Subject: [Bldg-sim] Modeling a Green Roof
>
>
>
>Howdy!
>
>
>
>Has anyone modeled a green roof? I have a
>standard roof with 12 inches of soil and grass.
>I have been searching the web for thermal
>properties such as U values, thermal
>absorptivity and so on. Are there any good
>references to find these values or does anyone
>have tips to model a green roof? I appreciate your help.
>
>
>
>
>
>Jason Boehning, EIT
>
>Mechanical Engineer
>
>Error! Filename not specified.
>
>6161 Savoy, Suite 1212
>
>Houston, Texas 77036
>
>
>
> v. 713.482.2322
>
> f. 713.482.2314
>
> e. <mailto:Jason.Boehning at ricegardner.com>Jason.Boehning at ricegardner.com
>
>
>
>_______________________________________________
>Bldg-sim mailing list
><http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a
>blank message to
><mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a
>blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
Chris Jones
14 Oneida Avenue
Toronto, ON M5J 2E3.
Tel. 416-203-7465
Fax. 416-946-1005
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100713/5bd0418c/attachment.htm>
More information about the Bldg-sim
mailing list