[Bldg-sim] TRACE modeling question - Heating Only

Snarski, Marty msnarski at shwgroup.com
Tue May 18 07:33:31 PDT 2010


Hello, everyone.

 

I've got a question that I've never been clear on and figured I'd turn
to the experts (you all).

 

In appendix G, Table G3.1.1b, it's stated that all conditioned spaces
shall be modeled as being both heated and cooled, even if no cooling
systems exists, for both the proposed and baseline buildings.

 

We typically place Cabinet Unit Heaters in stairways and vestibules, and
don't worry about cooling those spaces.  So, my question is, though
TRACE has a couple "Heating only" systems options, Appendix G says that
these cannot be selected.  So, what is a common solution?  The other
systems in the building are VAV, so, can those spaces just be grouped on
to there?

 

Thanks for any advice you'd have!

 

 

Martin Snarski   LEED(r) AP 
Mechanical Engineer 

SHWGROUP 



 



NOTICE:
This e-mail transmission is intended only for the use of the individual or entity named above and may contain information that is confidential, privileged, and/or exempt from disclosure under applicable law. If you are not the intended recipient, you are hereby notified that any review, disclosure, copying, distribution, or other use of any of the information contained in this transmission is strictly prohibited. If you have received this transmission in error, please immediately notify the sender by e-mail at the above address and delete it from your computer system; you should not copy the message or disclose its contents to anyone. The content of the message and or attachments may not reflect the view and opinions of the originating company or any party it is representing.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100518/be9d15d9/attachment.htm>


More information about the Bldg-sim mailing list