[Bldg-sim] TRACE modeling question - Heating Only
Fareed Syed
syedf at progressiveae.com
Tue May 18 07:35:51 PDT 2010
In my past experience, I had assigned those heated only spaces to VAV
systems for the baseline model. I think that's the most appropriate way
of complying Appendix G. And this way it went through without any
comments from the reviewer.
Thanks,
Fareed
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Snarski,
Marty
Sent: Tuesday, May 18, 2010 10:34 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] TRACE modeling question - Heating Only
Hello, everyone.
I've got a question that I've never been clear on and figured I'd turn
to the experts (you all).
In appendix G, Table G3.1.1b, it's stated that all conditioned spaces
shall be modeled as being both heated and cooled, even if no cooling
systems exists, for both the proposed and baseline buildings.
We typically place Cabinet Unit Heaters in stairways and vestibules, and
don't worry about cooling those spaces. So, my question is, though
TRACE has a couple "Heating only" systems options, Appendix G says that
these cannot be selected. So, what is a common solution? The other
systems in the building are VAV, so, can those spaces just be grouped on
to there?
Thanks for any advice you'd have!
Martin Snarski LEED(r) AP
Mechanical Engineer
SHWGROUP
NOTICE:
This e-mail transmission is intended only for the use of the individual
or entity named above and may contain information that is confidential,
privileged, and/or exempt from disclosure under applicable law. If you
are not the intended recipient, you are hereby notified that any review,
disclosure, copying, distribution, or other use of any of the
information contained in this transmission is strictly prohibited. If
you have received this transmission in error, please immediately notify
the sender by e-mail at the above address and delete it from your
computer system; you should not copy the message or disclose its
contents to anyone. The content of the message and or attachments may
not reflect the view and opinions of the originating company or any
party it is representing.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100518/574415e0/attachment-0001.htm>
More information about the Bldg-sim
mailing list