[Bldg-sim] EE4 Ground Source Heat Pumps
Oleksandra Onisko
oleksandra.onisko at ecovert.ca
Mon Nov 22 06:10:56 PST 2010
Thank you for all your help. It seems to be that the issue can be solved by
changing the room type from multi-residential to dorm-bedroom. This results
in a proper reference building with heating. I think this strategy is valid
under the EE4 modeling guidelines as this is the suggested way to take
credit for any hardwired efficient lighting in the suites. Of course some of
the defaults and schedules have to be reset to reflect the actual space
use...
___________________________________________
Oleksandra Onisko, B.A.Sc., LEED AP
Project Manager & Energy Modeler
ECOVERT | Sustainability Consultants
Office 416.350.2002
Direct Line 416.987.1105
Fax 416.766.5021
55 Ormskirk Avenue
Toronto, ON, M6S 4V6
www.ecovert.ca
On Sun, Nov 21, 2010 at 9:46 PM, Laurier Nichols <Laurier.Nichols at dessau.com
> wrote:
> Hi,
>
> Send me the input file (.bld) I will look try to help you. Are you using
> the EE-4 version 1.70 ?
>
> Salutations
>
>
>
> *LAURIER NICHOLS, ing.*
>
> Vice-président, Expertise
>
> Bâtiments
>
>
>
> *Dessau*
>
> 375, boul. Roland-Therrien, bureau 400
>
> Longueuil (Québec) J4H 4A6
>
> *T* 514.281.1033, poste 2526
>
> *F* 450.442.9996
>
> *C* laurier.nichols at dessau.com
>
> www.dessau.com <http://www.dessau.com%20>
>
>
> ------------------------------
>
> *De :* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *De la part de* Maudud Quazi
> *Envoyé :* 21 novembre, 2010 13:43
> *À :* Oleksandra Onisko
> *Cc :* bldg-sim at lists.onebuilding.org
> *Objet :* Re: [Bldg-sim] EE4 Ground Source Heat Pumps
>
>
>
> Hello Olenksandra,
>
>
>
> I also once got the same problem of getting negative savings. At that
> point I spoke to someone and he told me that probably I changed one default
> value which should be kept as is according to MNECB guidelines, such as
> schedule, room set temperature etc. However, I am not too sure about it. I
> hope someone else can give a better answer to your question.
>
>
>
> Regards,
>
>
>
> Hassan Quazi
>
> On Fri, Nov 19, 2010 at 1:06 PM, Oleksandra Onisko <
> oleksandra.onisko at ecovert.ca> wrote:
>
> Hello,
>
>
>
> I am trying to model a MURB with distributed heat pumps and a gas fired
> make-up air unit. The heat pump loop is attached to a ground field heat
> exchanger and a supplementary boiler. I am getting very strange results:
> the model is showing negative savings. Upon closer inspection, it seems like
> the reference building does not have any heating created. I have followed
> the instruction in the EE4 modelling guide...am I missing something?
>
>
>
> Regards,
>
> ___________________________________________
>
> Oleksandra Onisko, B.A.Sc <http://b.a.sc/>., LEED AP
> Project Manager & Energy Modeler
>
> ECOVERT | Sustainability Consultants
> Office 416.350.2002
> Direct Line 416.987.1105
> Fax 416.766.5021
> 55 Ormskirk Avenue
> Toronto, ON, M6S 4V6
> www.ecovert.ca
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> **********************************************************************
>
> Ce courriel et toute information qui y est jointe sont confidentiels et
> peuvent être assujettis au secret professionnel. Si vous l'avez reçu par
> inadvertance, détruisez-le et communiquez avec nous.
>
>
>
> This e-mail and any information enclosed are confidential and can be
> subject to professional secrecy. If you received it by mistake, destroy it
> and communicate with us.
>
>
>
> Este documento electrónico y toda información que se adjunta son
> confidenciales y pueden estar sometidos al secreto profesional. Si lo
> recibió por error, elimínelo y comuníquese con nosotros.
>
> **********************************************************************
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101122/c7c7257b/attachment-0002.htm>
More information about the Bldg-sim
mailing list