[Bldg-sim] G3.1.2.5 Clarification
Jon Matthews
jonmatthews10 at yahoo.com
Thu Oct 28 06:41:46 PDT 2010
Baseline building should always be just providing the minimum outdoor air
ventilation rate required by 62.1. It should never be increased. For proposed,
it just means that your OA should never be below the minimum OA requirement of
62.1. Now if the design chooses to pursue 30% more OA. Then you should reflect
in your model what is in the design. G3.1.2.5 just wants to make sure that you
do not model your proposed to be below the minimum OA. Providing 30% more OA can
earn you a credit but it will affect your EAc1.
Jon
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101028/d22164fd/attachment-0001.htm>
More information about the Bldg-sim
mailing list