[Bldg-sim] G3.1.2.5 Clarification
Rosenberg, Michael I
michael.rosenberg at pnl.gov
Thu Oct 28 07:05:33 PDT 2010
This changes with the soon to be released 90.1-2010 which adds the following;
If the minimum outdoor air intake flow in the proposed
design is provided in excess of the amount required by the
rating authority or building official then the baseline
building design shall be modeled to reflect the greater of
that required by the rating authority or building official
and will be less than the proposed design.
__________________________
Michael Rosenberg
Senior Commercial Buildings Energy Analyst
ENERGY & ENVIRONMENT DIRECTORATE
Pacific Northwest National Laboratory
2032 Todd Street
Eugene, OR 97405
(541) 844-1960
michael.rosenberg at pnl.gov<mailto:michael.rosenberg at pnl.gov>
www.pnl.gov<http://www.pnl.gov>
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Grammy
Sent: Thursday, October 28, 2010 5:38 AM
To: Jaigath Chandraprakash
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] G3.1.2.5 Clarification
In my opinion:
For LEED, the OA should increase 30% first. This is the propose requirement.
Then for energy model, the baseline model should equal to proposed, which means the baseline OA is also 30% more than 62.1 requirement.
On Thu, Oct 28, 2010 at 6:07 PM, Jaigath Chandraprakash <cjaigath at yahoo.com<mailto:cjaigath at yahoo.com>> wrote:
Hello,
G3.1.2.5 states that minimum ventilation rates will be the same for proposed building and baseline building. Does it mean that if my building design OA rate is increased by 30%, my model will still be based on the minimum OA required by 62.1 and is still equal to the baseline building OA? Meaning my proposed building wont be penalized by supplying more OA?
Thanks in advance.
Jaigath
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20101028/0eddeeb7/attachment-0002.htm>
More information about the Bldg-sim
mailing list