[Bldg-sim] Bldg-sim] Modeling tool for daylight, Energy, Thermal comfort analysis
Chris Yates
chris.malcolm.yates at gmail.com
Tue Apr 26 00:59:09 PDT 2011
Hi Gerfried,
Do you mean KTH Sweden? You said LTH! KTH do some work with Equa
Simulation AB and their system IDA ICE is very promising. The only item
on the list it doesn't tick is the daylighting - and only then if you
want output similar to Radiance. However, if you aren't interested in a
daylight map it does have a fully integrated window shading and daylight
model that interacts with the thermal simulation at runtime - like E+.
To my knowledge, I am not aware that IES satisfies window shading models
that interact with daylight controls at runtime - perhaps Pete Murray
could comment.
Best regards
Chris
On 25/04/2011 18:46, Radler63 wrote:
> Hello,
> we tried out a software named PARASOL, developed by LTH SWEDEN. but
> since we wanted to model rollable blinds with PV-included, adding also
> a special control agorithm, we did our own model in python.
> by using PARASOL you may do some postprocessing for the comfort
> factors. also may point you to Mathcad which allows to do all at a
> macroscopic level with the help of some existing code and WYSIWYG coding.
> best regards
> Gerfried
> Her is the project brief http://www.effiziente.st/sowa_en.htm
> and here a new questionnaire about building integrated solar
> http://www.surveymonkey.com/s/HHNBJ2B
> *From:* Jeff Haberl <mailto:jhaberl at tamu.edu>
> *Sent:* Monday, April 25, 2011 6:55 PM
> *To:* ali hamada fakra <mailto:fakra at univ-reunion.fr>
> *Cc:* bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>
> *Subject:* Re: [Bldg-sim] Bldg-sim] Modeling tool for daylight,
> Energy, Thermal comfort analysis
>
> Hamada,
>
> I did not mention nor comment on CODYRUN as I am not familiar with
> this software.
>
> jeff
>
> 8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) 8=() 8=) 8=| 8=) :=') 8=)8=?
>
> Jeff S. Haberl, Ph.D.,P.E., FASHRAE..............jhaberl at tamu.edu
>
> Professor............................................................Office
> Ph: 979-845-6507
>
> Department of Architecture.............................Lab Ph:979-845-6065
>
> Energy Systems Laboratory.............................FAX: 979-862-2457
>
> Texas A&M University.....................................77843-3581
>
> College Station, Texas, USA, 77843..................URL:www.esl.tamu.edu
>
> 8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) :=) 8=) 8=! 8=) 8=? 8=)8=0
> ------------------------------------------------------------------------
> *From:* ali hamada fakra [fakra at univ-reunion.fr]
> *Sent:* Monday, April 25, 2011 4:23 AM
> *To:* Jeff Haberl
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Bldg-sim] Modeling tool for daylight,
> Energy, Thermal comfort analysis
>
> Dear Prof. Haberl,
> Is that your remarks are addressed directlty to me ? is what I do
> understand that you criticize the software CODYRUN ? If this is not
> the case, I apologize to you for that question.
> best regards.
> A. H. Fakra
> Le 25 avr. 11 à 06:49, Jeff Haberl a écrit :
>
>> Hamada,
>> Unfortunately, you've chosen the worst possible building for
>> analysis. There are several reasons for this.
>> First, there is no single U.S. tool that does an accurate analysis of
>> what you are asking for. There are some that perform simplified
>> analysis of most of the parameters you are looking for, but none do
>> it all right (that I’m aware of). Some of the European codes are
>> getting close, for example ESPr and/or IES/VE, but each has its
>> limitations.
>> To estimate the thermal analysis with Visual DOE (i.e., DOE-2.1e) or
>> EQUEST (i.e., DOE-2.2) you’d need to have at least one zone that is
>> conditioned in order to simulate conditions in an unconditioned
>> space. So, although it is possible to perform such a simulation, you
>> have to go to great lengths to do this with canned simulations such
>> as DOE-2.1e and DOE-2.2. One successful project that did this for a
>> Buddhist temple was done by Dr. Sreshthaputra, which you can read
>> about in:
>> Sreshthaputra, A., Haberl, J., Andrews, M. 2004. “Improving Building
>> Design and Operation .of a Thai Buddhist Temple,”/Energy and
>> Buildings/, Vol. 36, pp. 481-494.
>> Or in his thesis:
>> Atch Sreshthaputra, 2004. “Building Design and Operation for
>> Improving Thermal Comfort in Naturally Ventilated Buildings in a Hot
>> and Humid Climate,” Department of Architecture, Texas A&M University.
>> In this work, which was calibrated to real data from the temple, Atch
>> created a fictitious zone that did nothing, then proceeded to model
>> the temple as a unconditioned zone, which worked with one exception
>> that it did not handle the air flows. To get around this Atch ran CFD
>> with a program that used a 3D model from the CHAM engine, then passed
>> the airflows back to DOE-2 each hour to do the run, which calculated
>> the dynamic heat transfer, then back to the CFD for the next hour’s
>> airflow, etc., (taking 24 hours to simulate 24 hours on 2003ish
>> Pentium, not exactly fast).
>> Second, you can probably get an estimate of the daylighting using
>> DOE-2.1e or DOE-2.2 that should be accurate for and sidelights if you
>> know the internal geometry, including surface characteristics, since
>> they use the split-flux method. More accurate daylighting simulations
>> can be done with RADIANCE or annual simulations with DAYSIM, or
>> perhaps one of the new annual variants of RADIANCE.
>> Third, true calculations of thermal comfort would require CFD and a
>> internal radiation network (should interior surfaces get hot or
>> cold), which further complicate things.
>> So, it can be done, but there are only a few efforts in the
>> literature that give solid advice on how to do this, probably more as
>> time goes on. Getting all this in one package is probably not there
>> yet. Probably still a good topic for a Ph.D. thesis.
>>
>> Jeff
>>
>> 8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) 8=() 8=) 8=| 8=) :=') 8=)8=?
>>
>> Jeff S. Haberl, Ph.D.,P.E., FASHRAE..............jhaberl at tamu.edu
>> <mailto:jhaberl at tamu.edu>
>>
>> Professor............................................................Office
>> Ph: 979-845-6507
>>
>> Department of Architecture.............................Lab
>> Ph:979-845-6065
>>
>> Energy Systems Laboratory.............................FAX: 979-862-2457
>>
>> Texas A&M University.....................................77843-3581
>>
>> College Station, Texas, USA,
>> 77843..................URL:www.esl.tamu.edu <http://www.esl.tamu.edu>
>>
>> 8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) :=) 8=) 8=! 8=) 8=? 8=)8=0
>> ------------------------------------------------------------------------
>> *From:*bldg-sim-bounces at lists.onebuilding.org
>> <mailto:bldg-sim-bounces at lists.onebuilding.org>[bldg-sim-bounces at lists.onebuilding.org
>> <mailto:bldg-sim-bounces at lists.onebuilding.org>] on behalf of ali
>> hamada fakra [fakra at univ-reunion.fr <mailto:fakra at univ-reunion.fr>]
>> *Sent:*Thursday, April 21, 2011 11:32 PM
>> *To:*bldg-sim at lists.onebuilding.org
>> <mailto:bldg-sim at lists.onebuilding.org>
>> *Subject:*[Bldg-sim] Bldg-sim] Modeling tool for daylight, Energy,
>> Thermal comfort analysis
>>
>> Message: 2
>> Date: Thu, 21 Apr 2011 10:47:20 +0530 (IST)
>> From: Rathna Shree <rathnashreep at yahoo.in <mailto:rathnashreep at yahoo.in>>
>> To: bldg <bldg-sim at lists.onebuilding.org
>> <mailto:bldg-sim at lists.onebuilding.org>>
>> Subject: [Bldg-sim] Modeling tool for daylight, Energy,Thermal
>> comfort analysis
>> Message-ID: <935834.21570.qm at web95906.mail.in.yahoo.com
>> <mailto:935834.21570.qm at web95906.mail.in.yahoo.com>>
>> Content-Type: text/plain; charset="utf-8"
>>
>> Dear All,
>>
>> Can you please suggest the best modeling tool which has the
>> capabilities to perform Daylight simulation, Thermal comfort analysis
>> in non AC spaces of a building and Energy simulation.
>>
>> I am using dialux for daylight simulation, Visual Doe for Energy
>> simulation and Transys for Thermal comfort analysis. I am inputting
>> the same details thrice in different softwares. So is there any
>> software which can perform all the 3 analysis in one go.
>>
>> Regards,
>> Rathnashree
>> ------------------------------------------------------------
>> Hello Rathmashree,
>> I suggest you use CODYRUN. Is a french software dedicated to both
>> research and consulting firms. You can make the 3 studies (Energy
>> simulation, Daylight and thermal confort).that you want at the same
>> time. For more information about this software, you can write to
>> Professor Harry Boyer (Founder of the software) to this mail :
>> harry.boyer at univ-reunion.fr <mailto:harry.boyer at univ-reunion.fr>
>> Best regards,
>> PhD / Engineer A. H. Fakra
>>
> ------------------------------------------------------------------------
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
--
Chris Yates C Eng MCIBSE
/Building Physics Consultant/
Tel:+447960731576
Email: chris.malcolm.yates at gmail.com
Skype: christopher.m.yates
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110426/74858f98/attachment-0002.htm>
More information about the Bldg-sim
mailing list