Hello Bldg Sim Folks,
Could anyone comment on how they "translate" the F-factor requirement for on grade slabs into a U-value / material for a floor construction in Energy+ or eQuest
My method has always been to create a fictional material with negligible thickness that approximates the equivalent R-value for the whole floor area of the zone based on the edge requirement. This results in me creating a separate one of these fictional materials for each zone. This is because even though a zone might have the same F-factor requirement the difference in perimeter to floor area ratio effects the actual heat flux through the floor, or so I think.
Here is an example of how I have modeled this, see attached picture for a layout:
[cid:image001.png at 01CC6249.A570F5C0]
F-Factor = 0.64 (equivalent to R-10 insulation for 48" and for an "Unheated Slab" per ASHRAE 90.1 Table A6.3)
Zone 1
Area = 25 sqft
Edge Perimeter = 10 ft
Zone 2
Area = 375 sqft
Edge Perimeter = 70 ft
Perimeter * F factor = Area * U value equivalent
Zone 1 equivalent U = 0.256
Zone 2 equivalent U = 0.119
This process has made sense to me, but in reviewing this technique with a colleague we wondered what does everyone else do. Am I under/over predicting slab loss for certain zones with this method? Your comments and insight are always appreciated.
Thanks,
Josh
Joshua W. Talbert P.E., LEED-AP
Mechanical Engineer
Hallam///ICS
38 Eastwood Dr. Suite 200
S. Burlington, VT 05403
P: (802) 658-4891
F: (802) 658-1457
________________________________
CONFIDENTIALITY NOTICE:
The information contained in this transmission, as well as any accompanying documents, constitutes confidential and/or legally privileged information which is the property of Hallam-ICS. The information is intended solely for the individual entity named on this transmittal sheet. If you are not the designated recipient, you are hereby notified that any disclosure, copying, distribution or taking any action in reliance on this information is strictly prohibited. If you received this in error, please contact the sender and delete the material from any computer. Opinions, conclusions and the information in this message that do not relate to the official business of my firm shall be understood as neither given nor endorsed by it.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110824/5b8b2437/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 10188 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110824/5b8b2437/attachment.png>
More information about the Bldg-sim
mailing list