[Bldg-sim] Comfort tools
Patrick J. O'Leary, Jr.
poleary1969 at gmail.com
Wed Jan 26 05:56:39 PST 2011
pretty much so if you're attempting to use to the ashrae comfort tools
to invidually "model" every space in a building. i am using it at the
system level only, more as a measure of setpoint/airflow to show a
compliance with ashrae 55 as the systems i typically work with are
simpler (i.e. smaller packaged units with not a lot of differentiation
in use met/clo per system).
the ashrae tool has its limitations but your question was about tools
that are specifically developed to perform only comfort calculations -
pmv, ppd, etc, - and that it does within the limitations of how it is
applied and what one is trying to use it for.
On 1/26/11 6:18 AM, Tariq Abbas wrote:
>
> Sounds impossible.
>
> Information in bulk zone modelling is only stored at the node
> (typically centre of zone) and on surfaces with no additional info in
> between.
>
> There are too many unknown parameters to determine thermal comfort in
> this way to determine a gradient.
>
> You would have to use CFD which can be tricky without experience of
> solar radiation modelling (depending on package used).
>
> *From:* bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Patrick
> J. O'Leary, Jr.
> *Sent:* 26 January 2011 02:53
> *To:* Arpan Bakshi
> *Cc:* bldg-sim at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] Comfort tools
>
> attached is a screenshot of the ashrae comfort tool output
>
>
>
> On 1/24/11 10:06 AM, Arpan Bakshi wrote:
>
> Comfort Gradients
>
> Are there other tools out there which are specifically developed to
> perform only comfort calculations, PMV, PPD, etc.?
>
> My understanding of the comfort models in DesignBuilder, ApacheSim
> other energy modeling engines is that they calculate comfort only at
> the central node of each thermal zone.
>
> Is anyone aware of tools which calculate a gradient of comfort
> within each thermal zone?
>
> Thanks
>
> Arpan
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message toBLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>
> ______________________________________________________________________
> This email has been scanned by the MessageLabs Email Security System.
> For more information please visit http://www.messagelabs.com/email
> ______________________________________________________________________
>
>
> ______________________________________________________________________
> This email has been scanned by the MessageLabs Email Security System.
> For more information please visit http://www.messagelabs.com/email
> ______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20110126/ec5ac943/attachment-0002.htm>
More information about the Bldg-sim
mailing list