Item 1 - the ESAF's are used in defining the reference building envelope
parameters -- that is why you must define the primary heating source for
each zone. In practise, you just use the energy consumption & costs
from EE4 to populate the LEED Canada letter template. The ESAF's are
not used in the EA-Cr 1 or EA Pr 2 calculations.
Item 2 - your interpretation is not correct. There is a document called
the Performance Compliance for Buildings which defines the reference
building (automatically generated by EE4). Roughly translated, the
reference building has a single 80% efficient boiler (if you have
hydronic heating in the proposed building, it has 1 or 2 chillers (2 if
your plant exceeds 700 tons) with a COP of 5.2. There are 3 reference
building types -- single zone, residential (hotels, dorms etc) ... and
everything else which has a VAV reference system type.
The MNECB is and old code very easy to beat. Standard design should be
25% better than the MNECB (due mainly to lighting). Good HVAC design
(e.g. condensing boilers, dedicated OA systems and ventilation heat
recovery) can put you 50 to 60% better than the MNECB. (My office is in
a building >75% better than the MNECB, but that is another story).
On 10/10/2011 3:11 PM, Anne M. Moellenberndt wrote:
>
> I'm looking for some feedback from anyone who has used EE4 and/or
> modeled a building against the MNECB 1997 in Canada.
>
> 1.How are the Energy Source Adjustment Factors used when modeling a
> building for LEED against the MNECB? It appears that these factors
> are meant to be multiplied by the total energy cost from each type of
> use. I see that at least in LEED Canada NC 1.0/1.1, the calculations
> for EQ p2 require 25% improvement in energy consumption (not cost)
> over MNECB. Presumably this requires use of the ESAF in that
> calculation. However, LEED also requires that calculations for energy
> savings are based on energy cost. When calculating energy costs, do
> you have to use the ESAF as well as the different utility rates? Or do
> you use the actual consumption (without using the ESAF) to figure the
> cost?
>
> 2.The code appears to require use of baseline systems that completely
> mirror the proposed systems -- boiler for boiler, chiller for chiller,
> multi-zone for multi-zone. How have others found ways to show
> significant energy savings given this constraint? The newer versions
> of ASHRAE allow comparison of a proposed ground-source heat pump
> system, for example, against a boiler heating baseline system, or a
> VAV system against a packaged system, depending on various factors.
> But the MNECB and ASHRAE 90.1-1999 don't allow this. I am struggling
> to see how it would be possible to get more than 20-30% savings given
> these rules.
>
> Thanks,
>
> *Anne Marie Moellenberndt *PE LEED AP**
>
> Senior Mechanical Engineer
>
> *Arup*
>
> 403 Columbia Street Suite 220 Seattle WA 98104
>
> *t*+1 206 749 9674 *d* +1 206 493 2244
>
> *f*+1 206 749 0665
>
> www.arup.com <http://www.arup.com/>
>
> ____________________________________________________________
> Electronic mail messages entering and leaving Arup business
> systems are scanned for acceptability of content and viruses
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> No virus found in this message.
> Checked by AVG - www.avg.com <http://www.avg.com>
> Version: 10.0.1410 / Virus Database: 1520/3943 - Release Date: 10/07/11
>
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1410 / Virus Database: 1520/3943 - Release Date: 10/07/11
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20111010/76fdca37/attachment-0002.htm>
More information about the Bldg-sim
mailing list