Dear Mr. Sharma,
You are correct that there are no outputs specific to the radiant loop
objects or the "InternalSource" constructions that will give you a surface
temperature. However, you should be able to grab any surface's temperature
with:
Output:Variable,
SURFACE NAME,
Surface Inside Temperature,
Daily OR Hourly;
Regards,
Peter
____________________________________
Peter May-Ostendorp, EIT, LEED AP
PhD Candidate
University of Colorado at Boulder
College of Engineering and Applied Sciences
Building Systems Program
M: 970.426.8827
Please think before printing.
On Dec 29, 2011, at 2:31 PM, <bldg-sim-request at lists.onebuilding.org> wrote:
Send Bldg-sim mailing list submissions to
bldg-sim at lists.onebuilding.org
To subscribe or unsubscribe via the World Wide Web, visit
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
or, via email, send a message with subject or body 'help' to
bldg-sim-request at lists.onebuilding.org
You can reach the person managing the list at
bldg-sim-owner at lists.onebuilding.org
When replying, please edit your Subject line so it is more specific
than "Re: Contents of Bldg-sim digest..."
<Today's Topics (1 messages).txt>
From: Sachin Sharma <sachin5787 at gmail.com>
Subject: [Bldg-sim] Radiant Floor Temperature in EnergyPlus
Date: December 29, 2011 4:59:44 AM MST
To: "'bldg-sim at lists.onebuilding.org'" <Bldg-sim at lists.onebuilding.org>
Hi,
I am modelling a radiant hydronic floor cooling system. I want to know the
floor temperature report on daily or hourly basis of my conditioned zone. I
have tried finding the option in Output:Variable object, but not able to
find it. Can anyone help me out.
Thanks,
With regards,
Sachin Sharma
M.Tech Energy Engg.
Department of Mechanical Engineering
NIT Jaipur
+91 9983912512
<Digest Footer.txt>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120102/b54efdf7/attachment.htm>
More information about the Bldg-sim
mailing list