[Bldg-sim] EE4 (DOE-2.1E) Water-Side Economizer Issue
Chris Jones
cj at enersave.ca
Wed Jul 25 05:23:00 PDT 2012
From the DOE2.1E Supplement:
DIRECT-COOL-KW
specifies the electrical input to direct cooling auxiliary equipment.
The default varies according to the direct cooling mode.
IT DIRECT-COOL-MODE = THERMO-CYCLE, you should
specify DIRECT-COOL-KW as kW /ton of operating capacity
for the period during which the compression chillers are operating
in this mode. The chiller electrical input is assumed to be
DIRECT-COOL-KW multiplied by the operating capacity
and the fraction of the hour the chiller ran. If
DIRECT-COOL-MODE = STRAINER-CYCLE, you should
specify DIRECT-COOL-KW as the electrical input to the
condenser water pumps (and other added equipment), calculated
as kW /ton of SYSTEMS peak cooling load. Usually, this
value is zero as the chilled water pumps are assumed to provide
all motive energy. If a heat exchanger is used to isolate the
tower from the chilled water loop, then this value should be
non-~ero to model the condenser pumping energy. In this case,
the condenser water pumping energy is calculated using the
value of DIRECT-COOL-KW as the kW per ton of the design
SYSTEMS load. (Fluid flow to the tower is assumed to be the
design chilled water flowrate). For both modes of direct cooling,
THERMO-CYCLE and STRAINER-CYCLE, the chilled
water pumps are assumed to run as usual.
At 01:35 PM 24/07/2012, Jake Martell wrote:
>Hello,
>
>-I am looking to simulate a water-side economizer in EE4 (DOE-2.1E)
>by altering the .doe file.
>-I have added the highlighted text below into the "Plant-Parameters"
>section of the .doe file.
>
>
>PLANT-PARAMETERS
> BOILER-CONTROL = STANDBY
> HW-BOILER-HIR = 1.0870
> CHILLER-CONTROL = STANDBY
>$ Cooling Tower $
> TWR-SETPT-CTRL = FIXED
> TWR-SETPT-T = 85.0
> TWR-DESIGN-WETBULB = 73.0
> TWR-DESIGN-APPROACH= 12.0
> TWR-DESIGN-RANGE = 10.0
> TWR-THROTTLE = 5
> TWR-CAP-CTRL = ONE-SPEED-FAN
> TWR-CELL-CTRL = MIN-CELLS
> DIRECT-COOL-MODE = STRAINER-CYCLE
> DC-MAX-OAT = 39.0
> DC-MAX-CHILL-WTR-T = 44.0
> DC-TWR-WTR-SETPT = 44.0
> DIRECT-COOL-KW = 0.055
>$ Condenser Water Pumps $
> TWR-MOTOR-EFF = 0.917
> TWR-IMPELLER-EFF = 0.790
> TWR-PUMP-HEAD = 60.00
> ..
>
>
>
>-After running the simulation and comparing it to previous results,
>there are savings on "Space Cooling" but there is also a greater
>energy usage in "Heat Reject" as show in the table below. The DOE-2
>guide suggests entering the condenser water pumping power as kW/ton
>but maybe I should be entering 0 for DIRECT-COOL-KW if I'm
>accounting for the condenser water pumps twice? This is for a
>project in Nova Scotia so I think there should be savings from
>turning off the chillers throughout the winter but it doesn't make
>sense based on these results.
>
>Energy Use Category
>Before Change
>After Change
>Savings
>
>
>
>(MBtu)
>(MBtu)
>(MBtu)
>% Sav
>
>Area Lights
>2,252.2
>2,252.2
>0
>0.0%
>
>Misc. Equipment
>1,629.1
>1,629.1
>0
>0.0%
>
>Space Heat
>2,062.0
>2,062.0
>0
>0.0%
>
>Space Cool
>615.6
>475.7
>140
>22.7%
>
>Heat Reject
>121.5
>295.6
>-174
>-143.3%
>
>Pumps & Misc.
>1,136.2
>1,136.2
>0
>0.0%
>
>Vent Fans
>2,168.4
>2,168.4
>0
>0.0%
>
>DomHot Water
>587.6
>587.6
>0
>0.0%
>
>TOTAL
>10,572.6
>10,606.8
>-34
>-0.3%
>
>
>
>Best regards,
>
>Jake R. Martell, EIT
>Mechanical Engineer-in-Training
>[]
>
>t: (902) 422-7393
>f: (902) 423-4945
>e: <mailto:jmartell at mreng.ca>jmartell at mreng.ca
>
>The electronic message contained herein is private and confidential,
>intended only for the recipient(s) specified. If you have received
>this message in error, please delete it and notify us immediately.
>Any accompanying files are supplied as a matter of courtesy only.
>The data are without warranty of any kind. Any person or business
>making use of the data is responsible for confirming its accuracy
>and completeness. M&R Engineering Ltd. is not responsible for edited
>or produced versions of this digital information.
>
>
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120725/8e173c2e/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 189da5.jpg
Type: application/octet-stream
Size: 1857 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120725/8e173c2e/attachment-0002.obj>
More information about the Bldg-sim
mailing list