[Bldg-sim] [EnergyPlus_Support] Food for thought....
Joe Huang
yjhuang at whiteboxtechnologies.com
Thu Jun 28 13:13:49 PDT 2012
Jim,
Sorry if I came off as a little smug. You've actually put in words the main reason why I
think building energy modelers have steered away from using historical weather data, which
is simply that of convenience, i.e., there are a lot of "typical year" weather files
floating around, but getting hold of
a usable historical year weather file takes a little more work.
For the study that I mentioned, Dru and I did not have to do anything because the SANSOM
data set,
available from NCDC, contained 25 years of historical weather files for 239 cities (same
as TMY2s).
That was in 1996, and the availability of historical weather data has only increased
exponentially since
then, although the building energy modeling community seems curiously to not have followed.
The most notable change, in my view, is NCDC's decision to put the entire ISH (Integrated
Surface Hourly) data online in 2005, and then to make it free to all in 2011. This means
that the raw weather reports
from major stations around the world ( ~ 1,500 in the US) are available stretching back to
1980.
I've been working with the ISH for many years now, and am able to generate complete
weather files from any ISH file within seconds, and have been providing that as a service
to customers. Sometime later this
year, I'll be rolling out something on the Web, but for now, those interested can just
send me an e-mail.
The idea that the ISH is of questionable quality is, in my view, rather backwards. The
ISH is a repository of the weather reports by the "official" weather stations around the
world, so if you can't trust that, what can you trust?
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 6/28/2012 11:48 AM, Jim Dirkes wrote:
>
> Dear Joe,
>
> No fair! You and Dru have been at the forefront energy modeling research for most of my
> adult life, and have a big head start.
>
> My guess is that you spent a lot of time preparing the actual weather files for the
> research, however. Unless I'm missing something, the ready availability of high quality
> (e.g., no big hunks of missing data) actual weather data has been pretty limited until
> recently. With folk like Weather Analytics getting on board and making it pretty easy
> to get and inexpensive, it becomes a lot faster and lower cost than trying to clean some
> of the NOAA / NCDC data, not to mention getting good data for sites not in or near a
> major city.
>
> Kudos for being way ahead of the industry curve (at least my own curve)! It's getting
> easier to catch up!
>
> p.s., Dru sent me that paper and I'll be reading it with interest very soon.
>
> *From:*Joe Huang [mailto:yjhuang at whiteboxtechnologies.com]
> *Sent:* Thursday, June 28, 2012 1:53 PM
> *To:* EnergyPlus_Support at yahoogroups.com
> *Cc:* Jim Dirkes; bldg-sim at lists.onebuilding.org
> *Subject:* Re: [EnergyPlus_Support] Food for thought....
>
> I've always thought it was a "no-brainer" to use actual weather data whenever you're
> comparing simulation results to actual consumption data. Even with the earliest
> degree-day software such as
> PRISM (Princeton Scorekeeping Method) in the 1980's, it was stressed to use the degree days
> from the period of record, and not the long-term average, so I'm not sure why this
> (using actual
> year weather data) is such a revelation.
>
> The variation in total energy consumption of course depends a lot on the building
> characteristics.
> Back in 1996, Dru Crawley and I wrote a paper on "Does it matter which weather data you
> use in energy simulations?", for the ACEEE Summer Study on Energy Efficiency in
> Buildings (it also appeared as two
> separate ASHRAE papers at around the same time) where we took some prototypical building
> models (Dru did commercial, I did residential) and ran them with various "typical year"
> weather files and also 25 years of historical data in 10-12 US locations.
>
> Joe
>
> Joe Huang
> White Box Technologies, Inc.
> 346 Rheem Blvd., Suite 108D
> Moraga CA 94556
> yjhuang at whiteboxtechnologies.com <mailto:yjhuang at whiteboxtechnologies.com>
> www.whiteboxtechnologies.com <http://www.whiteboxtechnologies.com>
> (o) (925)388-0265
> (c) (510)928-2683
> "building energy simulations at your fingertips"
>
>
> On 6/28/2012 8:49 AM, Jim Dirkes wrote:
>
> Dear Forums,
>
> I am busy preparing a short talk for the Fall ASHRAE Energy Modeling Conference. The
> topic is "An Approach for Calibrating Existing Building Energy Models to their Utility
> Consumption".
>
> As part of the preparation, I will address the issue of how muc h difference might
> result in energy conservation measure savings predictions if you use actual weather data
> for the billing period versus TMY data.
>
> To get a rough idea how much variation there might be, I looked at Degree Days for a
> span of years. What a variation! (for the city I'm studying at least)
>
> I am not yet sure how that affects total energy consumption -- you'll have to attend my
> presentation in Atlanta to find out J.
>
> In the meantime, I am starting to think that existing building energy models should use
> actual weather, not TMY data. Have any of you run similar comparisons for existing
> building models?
>
> __._,_.___
> Reply to sender
> <mailto:jim at buildingperformanceteam.com?subject=RE%3A%20%5BEnergyPlus_Support%5D%20Food%20for%20thought%2E%2E%2E%2E>
> | Reply to group
> <mailto:EnergyPlus_Support at yahoogroups.com?subject=RE%3A%20%5BEnergyPlus_Support%5D%20Food%20for%20thought%2E%2E%2E%2E>
> | Reply via web post
> <http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJxbWQ1aGMwBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzI1NDc4BHNlYwNmdHIEc2xrA3JwbHkEc3RpbWUDMTM0MDkwOTMyNA--?act=reply&messageNum=25478>
> | Start a New Topic
> <http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJlaTg2cmxwBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA250cGMEc3RpbWUDMTM0MDkwOTMyNA-->
>
> Messages in this topic
> <http://groups.yahoo.com/group/EnergyPlus_Support/message/25471;_ylc=X3oDMTM2bzRuMTh2BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzI1NDc4BHNlYwNmdHIEc2xrA3Z0cGMEc3RpbWUDMTM0MDkwOTMyNAR0cGNJZAMyNTQ3MQ-->
> (4)
> Recent Activity:
>
> * New Members
> <http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmM2I3aW5hBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzNDA5MDkzMjQ-?o=6>
> 14
>
> Visit Your Group
> <http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlNDRxczRnBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM0MDkwOTMyNA-->
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support at gard.com
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed
> connection. Limit attachments to small files.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation
> link and press the "search" button.
> Yahoo! Groups
> <http://groups.yahoo.com/;_ylc=X3oDMTJkZG5iZzA4BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzQwOTA5MzI0>
>
> Switch to: Text-Only
> <mailto:EnergyPlus_Support-traditional at yahoogroups.com?subject=Change%20Delivery%20Format:%20Traditional>,
> Daily Digest
> <mailto:EnergyPlus_Support-digest at yahoogroups.com?subject=Email%20Delivery:%20Digest> .
> Unsubscribe <mailto:EnergyPlus_Support-unsubscribe at yahoogroups.com?subject=Unsubscribe>
> . Terms of Use <http://docs.yahoo.com/info/terms/>
> .
>
> __,_._,___
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120628/7912e619/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 48474 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120628/7912e619/attachment-0002.png>
More information about the Bldg-sim
mailing list