[Bldg-sim] [EnergyPlus_Support] Food for thought....
Chris Jones
cj at enersave.ca
Thu Jun 28 15:44:41 PDT 2012
The discussion has become two discussions -
weather data and processing. And calibrating to
TRY (what I call acutal weather data for the same
billing period) or TMY, tyipcal weather data.
Environment had a number of weather stations with
hourly data - some with full weather data and
some with only a few data channels. Some
stations were daytime hours only. One had to
request a period of data and pay a setup
fee. The setup fee was more than the data fee so
it paid to request a bunch of sites at the same time.
We have an old C-code processor that converts the
EC data into an old DOE2.1e format text format
for conversion to a .WTH binary weather
file. The processor could use a number of
different channels depending on the weather
site. The input file signalled what channels
were coming in the text file. The Hirsh
processor can convert .WTH files to .bin files.
Environment Canada now has hourly data available
for much fewer sites. Cut backs closed dozens of
sites across the country. There is a significant
difference in weather between places like
Revelstoke and the closest site with TMY
weather. With the availability of stations
smaller places, one could aggregate a weather
file that captured the differences in temperature and humidity at least.
The good thing to happen with Environment Canada
is that the WEB site makes hourly data available
on line for a large number of stations across the
country. You can download a month at a time to a
.csv file. We now have a spreadsheet with the
appropriate psychometric functions that converts
the EC data to TRY data. We just save the data
to a text file for the Hirsh weather processor.
We use these TRY files for M&V projects.
At 04:13 PM 28/06/2012, Joe Huang wrote:
>Jim,
>
>Sorry if I came off as a little smug. You've
>actually put in words the main reason why I
>think building energy modelers have steered away
>from using historical weather data, which is
>simply that of convenience, i.e., there are a
>lot of "typical year" weather files floating around, but getting hold of
>a usable historical year weather file takes a little more work.
>
>For the study that I mentioned, Dru and I did
>not have to do anything because the SANSOM data set,
>available from NCDC, contained 25 years of
>historical weather files for 239 cities (same as TMY2s).
>
>That was in 1996, and the availability of
>historical weather data has only increased exponentially since
>then, although the building energy modeling
>community seems curiously to not have followed.
>The most notable change, in my view, is NCDC's
>decision to put the entire ISH (Integrated
>Surface Hourly) data online in 2005, and then to
>make it free to all in 2011. This means that the raw weather reports
>from major stations around the world ( ~ 1,500
>in the US) are available stretching back to 1980.
>
>I've been working with the ISH for many years
>now, and am able to generate complete weather
>files from any ISH file within seconds, and have
>been providing that as a service to customers. Sometime later this
>year, I'll be rolling out something on the Web,
>but for now, those interested can just send me an e-mail.
>
>The idea that the ISH is of questionable quality
>is, in my view, rather backwards. The ISH is a
>repository of the weather reports by the
>"official" weather stations around the world, so
>if you can't trust that, what can you trust?
>
>Joe
>
>
>Joe Huang
>White Box Technologies, Inc.
>346 Rheem Blvd., Suite 108D
>Moraga CA 94556
><mailto:yjhuang at whiteboxtechnologies.com>yjhuang at whiteboxtechnologies.com
>www.whiteboxtechnologies.com
>(o) (925)388-0265
>(c) (510)928-2683
>"building energy simulations at your fingertips"
>
>On 6/28/2012 11:48 AM, Jim Dirkes wrote:
>>
>>
>>Dear Joe,
>>
>>No fair! You and Dru have been at the
>>forefront energy modeling research for most of
>>my adult life, and have a big head start.
>>
>>My guess is that you spent a lot of time
>>preparing the actual weather files for the
>>research, however. Unless Im missing
>>something, the ready availability of high
>>quality (e.g., no big hunks of missing data)
>>actual weather data has been pretty limited
>>until recently. With folk like Weather
>>Analytics getting on board and making it pretty
>>easy to get and inexpensive, it becomes a lot
>>faster and lower cost than trying to clean some
>>of the NOAA / NCDC data, not to mention getting
>>good data for sites not in or near a major city.
>>
>>Kudos for being way ahead of the industry curve
>>(at least my own curve)! Its getting easier to catch up!
>>
>>p.s., Dru sent me that paper and Ill be reading it with interest very soon.
>>
>>
>>
>>From: Joe Huang
>>[<mailto:yjhuang at whiteboxtechnologies.com>mailto:yjhuang at whiteboxtechnologies.com]
>>
>>Sent: Thursday, June 28, 2012 1:53 PM
>>To:
>><mailto:EnergyPlus_Support at yahoogroups.com>EnergyPlus_Support at yahoogroups.com
>>Cc: Jim Dirkes;
>><mailto:bldg-sim at lists.onebuilding.org>bldg-sim at lists.onebuilding.org
>>Subject: Re: [EnergyPlus_Support] Food for thought....
>>
>>
>>
>>I've always thought it was a "no-brainer" to
>>use actual weather data whenever you're
>>comparing simulation results to actual
>>consumption data. Even with the earliest degree-day software such as
>>PRISM (Princeton Scorekeeping Method) in the
>>1980's, it was stressed to use the degree days
>>from the period of record, and not the
>>long-term average, so I'm not sure why this (using actual
>>year weather data) is such a revelation.
>>
>>The variation in total energy consumption of
>>course depends a lot on the building characteristics.
>>Back in 1996, Dru Crawley and I wrote a paper
>>on "Does it matter which weather data you use
>>in energy simulations?", for the ACEEE Summer
>>Study on Energy Efficiency in Buildings (it also appeared as two
>>separate ASHRAE papers at around the same time)
>>where we took some prototypical building models
>>(Dru did commercial, I did residential) and ran
>>them with various "typical year" weather files
>>and also 25 years of historical data in 10-12 US locations.
>>
>>Joe
>>
>>
>>Joe Huang
>>White Box Technologies, Inc.
>>346 Rheem Blvd., Suite 108D
>>Moraga CA 94556
>><mailto:yjhuang at whiteboxtechnologies.com>yjhuang at whiteboxtechnologies.com
>>www.whiteboxtechnologies.com
>>(o) (925)388-0265
>>(c) (510)928-2683
>>"building energy simulations at your fingertips"
>>
>>On 6/28/2012 8:49 AM, Jim Dirkes wrote:
>>
>>
>>
>>Dear Forums,
>>
>>I am busy preparing a short talk for the Fall
>>ASHRAE Energy Modeling Conference. The topic
>>is An Approach for Calibrating Existing
>>Building Energy Models to their Utility Consumption.
>>
>>As part of the preparation, I will address the
>>issue of how muc h difference might result in
>>energy conservation measure savings predictions
>>if you use actual weather data for the billing period versus TMY data.
>>
>>To get a rough idea how much variation there
>>might be, I looked at Degree Days for a span of
>>years. What a variation! (for the city Im studying at least)
>>
>>I am not yet sure how that affects total energy
>>consumption youll have to attend my presentation in Atlanta to find out J.
>>
>>In the meantime, I am starting to think that
>>existing building energy models should use
>>actual weather, not TMY data. Have any of you
>>run similar comparisons for existing building models?
>>
>>[]
>>
>>
>>__._,_.___
>><mailto:jim at buildingperformanceteam.com?subject=RE%3A%20%5BEnergyPlus_Support%5D%20Food%20for%20thought%2E%2E%2E%2E>Reply
>>to sender |
>><mailto:EnergyPlus_Support at yahoogroups.com?subject=RE%3A%20%5BEnergyPlus_Support%5D%20Food%20for%20thought%2E%2E%2E%2E>Reply
>>to group |
>><http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJxbWQ1aGMwBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzI1NDc4BHNlYwNmdHIEc2xrA3JwbHkEc3RpbWUDMTM0MDkwOTMyNA--?act=reply&messageNum=25478>Reply
>>via web post |
>><http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJlaTg2cmxwBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA250cGMEc3RpbWUDMTM0MDkwOTMyNA-->Start
>>a New Topic
>><http://groups.yahoo.com/group/EnergyPlus_Support/message/25471;_ylc=X3oDMTM2bzRuMTh2BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzI1NDc4BHNlYwNmdHIEc2xrA3Z0cGMEc3RpbWUDMTM0MDkwOTMyNAR0cGNJZAMyNTQ3MQ-->Messages
>>in this topic (4)
>>Recent Activity:
>> *
>> <http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmM2I3aW5hBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzNDA5MDkzMjQ-?o=6>New
>> Members 14
>><http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlNDRxczRnBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM0MDkwOTMyNA-->Visit
>>Your Group
>>Primary EnergyPlus support is found at:
>><http://energyplus.helpserve.com>http://energyplus.helpserve.com
>>or send a message to
>><mailto:energyplus-support at gard.com>energyplus-support at gard.com
>>
>>The primary EnergyPlus web site is found at:
>><http://www.energyplus.gov>http://www.energyplus.gov
>>
>>The group web site is:
>><http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
>>
>>Attachments are currently allowed but be
>>mindful that not everyone has a high speed
>>connection. Limit attachments to small files.
>>
>>EnergyPlus Documentation is searchable. Open
>>EPlusMainMenu.pdf under the Documentation link and press the "search" button.
>>Switch to:
>><mailto:EnergyPlus_Support-traditional at yahoogroups.com?subject=Change%20Delivery%20Format:%20Traditional>Text-Only,
>><mailto:EnergyPlus_Support-digest at yahoogroups.com?subject=Email%20Delivery:%20Digest>Daily
>>Digest
>><mailto:EnergyPlus_Support-unsubscribe at yahoogroups.com?subject=Unsubscribe>Unsubscribe
>> <http://docs.yahoo.com/info/terms/>Terms of Use
>>.
>>
>>__,_._,___
>
>
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a
>blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>
Christopher Jones, P.Eng.
Suite 1801, 1 Yonge Street
Toronto, ON M5E1W7
Tel. 416-203-7465
Fax. 416-946-1005
email cj at enersave.ca
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120628/83a94a77/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 77652f6.jpg
Type: application/octet-stream
Size: 181472 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20120628/83a94a77/attachment-0002.obj>
More information about the Bldg-sim
mailing list