[Bldg-sim] converting CDD from Celsius to Fahrenheit
Larry Degelman
ldegelman at suddenlink.net
Sat Oct 27 08:26:43 PDT 2012
Assuming you’re referring to degree day bases that are exactly equal (e.g. “50F and 10C” or “68F and 20C”, then the conversion should be simply HDDF = 1.8 * HDDC and CDDF = 1.8 * CDDC, since the values are incremental above a base temperature and not an absolute temperature. In a literal sense, these are actually Rankine DD and Kelvin DD respectively.
Larry Degelman
Professor Emeritus of Architecture
Texas A&M University.
==========================
From: Christian Stalberg
Sent: Saturday, October 27, 2012 8:54 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] converting CDD from Celsius to Fahrenheit
Can anyone tell me what the conversion equation would be for going from cooling degree days in Celsius to same in Fahrenheit?