[Bldg-sim] Setback Temperature
West, Scott P
Scott.West at jacobs.com
Mon Dec 2 15:07:10 PST 2013
Anderson,
I was checking this out recently I don't believe temperature or humidity setpoints are regulated by ASHRAE 90.1 during occupied periods. I think they primarily limit this through ASHRAE 55 regarding thermal comfort. Of course ASHRAE standard 55 is often not mandatory but it is certainly good practice. It goes without saying that several space types such as hospitals and labs have special temperature and humidity requirements that are industry-specific.
Scott P. West, P.E., LEED AP BD+C, BEAP, BEMP | JACOBS | Mechanical Engineer | Energy & Power Solutions | 817.222.8512 office | 817.897.1882 cell | scott.west at jacobs.com<mailto:rick.zilar at jacobs.com> | www.jacobs.com<http://www.jacobs.com/> | www.jacobs.com/energyportfolio<http://www.jacobs.com/energyportfolio>
From: Anderson Letti [mailto:anderson.a.letti at gmail.com]
Sent: Thursday, November 28, 2013 2:36 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Setback Temperature
Dear all,
We are working on a project that has a special occupancy space and we need to determine a setback/setup temperature for moments that the space is not occupied during working hours.
Section 6.4.3.3.2, of ASHRAE 90.1, states that setback temperature must be 13ºC or lower, and setup temperature, 32ºC or higher. I understand these temperatures are for off-hours.
Are there such limits of setback/setup temperature for working hours? Or is it defined by design?
Regards,
Anderson Letti
________________________________
NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131202/e8b994c1/attachment.htm>
More information about the Bldg-sim
mailing list