[Bldg-sim] ASHRAE 90.1 baseline HVAC sytem description
Santiago Velez
santiagogvelez at gmail.com
Wed Dec 11 07:31:53 PST 2013
I Agree with the interpretation, baseline (5 to 8) should be modelled with
one AHU system per unique floor. If say, the office building had 15
identical floors, then you would have three AHUs. first and last floor
would have different boundary conditions to the rest, so the simplified way
to model the baseline would be One AHU system for the first floor one for
the middle identical floors (with a load multiplier of 13) and one for the
last floor.
Santiago.
2013/12/11 Duggin, Cory <Cory.Duggin at tlc-eng.com>
> Yes, for ASHRAE 90.1-2007 and 2010 you will have 15 separate VAV AHUs (one
> per floor) in the baseline. I’m not sure of the reasoning for the change
> unless it is simply for standardization of the number of baseline systems.
>
>
>
> *Cory Duggin, EI*
>
> *Energy Engineer I*
>
> direct: 615-346-1939
>
>
>
>
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Linda Lam
> *Sent:* Wednesday, December 11, 2013 9:14 AM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] ASHRAE 90.1 baseline HVAC sytem description
>
>
>
> All,
>
>
>
> Can anyone share their experience with the modified baseline model HVAC
> description in ASHRAE 90.1 - 2007 and 2010? (copied below) ASHRAE
> 90.1-2004 did not require the baseline model for systems 5,6,7 and 8 to
> have separate HVAC systems *per floor* and I’d like to hear how people
> have interpreted this and, if anyone can explain the reasoning for this.
>
>
>
> For example, the proposed model of a 15 story office building might have 2
> AHUs, one serving the east wing and one serving the west wing. For the
> baseline per ASHRAE 90.1-2007 or 2010, will these 2 AHUs be replaced with
> 15 separate VAV units? Or can the 2 AHUs be kept as long as it satisfies
> the statement “Floors with identical thermal blocks can be grouped for
> modeling purposes”?
>
>
>
> ASHRAE 90.1 - 2004
>
> G3.1.1 *Baseline HVAC System Type and Description.*
>
> HVAC systems in the *baseline building design *shall be based
>
> on usage, number of floors, conditioned floor area, and heating
>
> source as specified in Table G3.1.1A and shall conform
>
> with the system descriptions in Table G3.1.1B.
>
>
>
> ASHRAE 90.1 – 2007 and 2010
>
> G3.1.1 *Baseline HVAC System Type and Description.*
>
> HVAC systems in the *baseline building design *shall be based
>
> on usage, number of floors, conditioned floor area, and heating
>
> source as specified in Table G3.1.1A and shall conform
>
> with the system descriptions in Table G3.1.1B. For systems 1,
>
> 2, 3, and 4, each thermal block shall be modeled with its own
>
> HVAC system. For systems 5, 6, 7, and 8, each floor shall be
>
> modeled with a separate HVAC system. Floors with identical
>
> thermal blocks can be grouped for modeling purposes.
>
>
>
> Thanks!
>
>
>
> Linda Lam
>
> 212 219 2255 | lam at transsolar.com
>
> Transsolar Inc. | 134 Spring St. Suite 601 | New York, NY 10012
>
>
>
> Transsolar Climate Engineering
>
> Technical consulting for energy efficiency and environmental quality in
> buildings
>
> New York - Stuttgart - Munich - Paris
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131211/b688d0ae/attachment-0002.htm>
More information about the Bldg-sim
mailing list