[Bldg-sim] ASHRAE 90.1 baseline HVAC sytem description
Nick Caton
ncaton at smithboucher.com
Wed Dec 11 13:48:59 PST 2013
I agree with the interpretation, paraphrased for clarity's sake: 15 separate baseline systems (one per floor), each with a number of VAV terminal units equal to the number of thermal blocks per floor (one per zone).
I speculate prior to 2007 folks (myself included) would generally match the quantity and arrangement of proposed systems where possible for baseline modeling. Without the direction of "one per floor" it would mean, all else being equal, two different baseline models could have varying performance based solely on the design of the proposed systems... I speculate the 90.1 committee didn't want the baseline systems to influence/inform actual designs in such a fashion, so they chose to lock down system quantities using the "one per floor" language. Arbitrary, yeah, but probably has a net effect of making baselines more uniform in performance across projects. That's my best guess, fwiw.
I would add to Jim/Santiago's multiplier suggestion that while floor/system multipliers are something I'd also expect to use for a 15-story building, assuming you can arrange for identical zoning and so forth, you may find it less work on the documentation/review side of things to model each floor & system separately. I caution this as I've run into reviewers needing hand-holding to understand what DOE2 system reports should look like when floor multipliers are in play, and I've also found on the front-end that baseline system calculations can become more complex considering the goal to clearly document how you arrived at your answers. To be fair, more complex calculations for half as many (or fewer) systems in quantity can balance out and may be a wash too.
Food for thought - hope that helps =),
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Santiago Velez
Sent: Wednesday, December 11, 2013 9:32 AM
To: Duggin, Cory
Cc: bldg-sim at lists.onebuilding.org; Linda Lam
Subject: Re: [Bldg-sim] ASHRAE 90.1 baseline HVAC sytem description
I Agree with the interpretation, baseline (5 to 8) should be modelled with one AHU system per unique floor. If say, the office building had 15 identical floors, then you would have three AHUs. first and last floor would have different boundary conditions to the rest, so the simplified way to model the baseline would be One AHU system for the first floor one for the middle identical floors (with a load multiplier of 13) and one for the last floor.
Santiago.
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jim Dirkes
Sent: Wednesday, December 11, 2013 9:30 AM
To: Duggin, Cory; Linda Lam; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] ASHRAE 90.1 baseline HVAC sytem description
I ALWAYS model using the "Floors with identical thermal blocks can be grouped for modeling purposes" allowance, as long as it's thermodynamically appropriate.
Same operating schedule on all 15 floors? Same setpoints? Same plug loads and lighting? What difference would it make to model 15 separate air handlers? (none)
One of my assessment criteria is "Can I explain what I did in front of a group of peers and expect that they'll agree with what I did?" In this case, I think it would be very hard for them to disagree.
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
2013/12/11 Duggin, Cory <Cory.Duggin at tlc-eng.com<mailto:Cory.Duggin at tlc-eng.com>>
Yes, for ASHRAE 90.1-2007 and 2010 you will have 15 separate VAV AHUs (one per floor) in the baseline. I'm not sure of the reasoning for the change unless it is simply for standardization of the number of baseline systems.
Cory Duggin, EI
Energy Engineer I
direct: 615-346-1939
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of Linda Lam
Sent: Wednesday, December 11, 2013 9:14 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] ASHRAE 90.1 baseline HVAC sytem description
All,
Can anyone share their experience with the modified baseline model HVAC description in ASHRAE 90.1 - 2007 and 2010? (copied below) ASHRAE 90.1-2004 did not require the baseline model for systems 5,6,7 and 8 to have separate HVAC systems per floor and I'd like to hear how people have interpreted this and, if anyone can explain the reasoning for this.
For example, the proposed model of a 15 story office building might have 2 AHUs, one serving the east wing and one serving the west wing. For the baseline per ASHRAE 90.1-2007 or 2010, will these 2 AHUs be replaced with 15 separate VAV units? Or can the 2 AHUs be kept as long as it satisfies the statement "Floors with identical thermal blocks can be grouped for modeling purposes"?
ASHRAE 90.1 - 2004
G3.1.1 Baseline HVAC System Type and Description.
HVAC systems in the baseline building design shall be based
on usage, number of floors, conditioned floor area, and heating
source as specified in Table G3.1.1A and shall conform
with the system descriptions in Table G3.1.1B.
ASHRAE 90.1 - 2007 and 2010
G3.1.1 Baseline HVAC System Type and Description.
HVAC systems in the baseline building design shall be based
on usage, number of floors, conditioned floor area, and heating
source as specified in Table G3.1.1A and shall conform
with the system descriptions in Table G3.1.1B. For systems 1,
2, 3, and 4, each thermal block shall be modeled with its own
HVAC system. For systems 5, 6, 7, and 8, each floor shall be
modeled with a separate HVAC system. Floors with identical
thermal blocks can be grouped for modeling purposes.
Thanks!
Linda Lam
212 219 2255 | lam at transsolar.com<mailto:lam at transsolar.com>
Transsolar Inc. | 134 Spring St. Suite 601 | New York, NY 10012
Transsolar Climate Engineering
Technical consulting for energy efficiency and environmental quality in buildings
New York - Stuttgart - Munich - Paris
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131211/47c09565/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20131211/47c09565/attachment-0002.jpg>
More information about the Bldg-sim
mailing list