[Bldg-sim] Automatic Generation of Baseline Models
Jim Dirkes
jim at buildingperformanceteam.com
Thu Feb 7 09:13:27 PST 2013
I think you need to define "automatically" carefully.
DesignBuilder does a fair amount of the work and Simergy intends to do something similar.
As an example, the proper ASHRAE 90.1 EER / COP is not known until you actually run the simulation and find out the capacity. It seems to me that some of the criteria must be ascertained from a successful simulation before you can have a complete Baseline.
Another example that has been discussed in this forum is calculating the proper fan and pump pressure rise to comply with 90.1
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jeremiah Crossett
Sent: Thursday, February 07, 2013 12:07 PM
To: Rosenberg, Michael I
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
Bentley havacomp AECOSIM does for one..
Jeremiah D. Crossett | Senior Analyst | Phase Change Energy Solutions
120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951
www.phasechange.com<http://www.phasechange.com>
[http://i.imgur.com/Sldxf.jpg]
On Thu, Feb 7, 2013 at 9:04 AM, Rosenberg, Michael I <michael.rosenberg at pnnl.gov<mailto:michael.rosenberg at pnnl.gov>> wrote:
I am hoping the building simulation community can help answer a question for me. What software packages out there automatically generate baseline models for the ASHRAE 90.1 Energy Cost Budget Methodology or Appendix G? Thanks.
__________________________
Michael Rosenberg, CEM, LEED AP
Senior Research Scientist
ENERGY & ENVIRONMENT DIRECTORATE
Pacific Northwest National Laboratory
2032 Todd Street
Eugene, OR 97405
(541) 844-1960<tel:%28541%29%20844-1960>
michael.rosenberg at pnnl.gov<mailto:michael.rosenberg at pnl.gov>
www.pnnl.gov<http://www.pnl.gov/>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/a6af9f98/attachment-0002.htm>
More information about the Bldg-sim
mailing list