Anybody tried the E+ example file generator. I found a minor issue with
it's PTAC definition but worth a look in.
http://apps1.eere.energy.gov/buildings/energyplus/cfm/inputs/
Chris
On 07/02/2013 21:18, Tianzhen Hong wrote:
> Mike,
>
> EnergyPro does that.
>
> Tianzhen
>
> On Thu, Feb 7, 2013 at 1:00 PM,
> <bldg-sim-request at lists.onebuilding.org
> <mailto:bldg-sim-request at lists.onebuilding.org>> wrote:
>
> Send Bldg-sim mailing list submissions to
> bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org>
>
> To subscribe or unsubscribe via the World Wide Web, visit
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> or, via email, send a message with subject or body 'help' to
> bldg-sim-request at lists.onebuilding.org
> <mailto:bldg-sim-request at lists.onebuilding.org>
>
> You can reach the person managing the list at
> bldg-sim-owner at lists.onebuilding.org
> <mailto:bldg-sim-owner at lists.onebuilding.org>
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Bldg-sim digest..."
>
>
> Today's Topics:
>
> 1. Penetration of energy modeling in new construction
> (Christoph Reinhart)
> 2. Automatic Generation of Baseline Models (Rosenberg, Michael I)
> 3. Re: Automatic Generation of Baseline Models (Jeremiah Crossett)
> 4. Re: Automatic Generation of Baseline Models (Jim Dirkes)
> 5. Re: Automatic Generation of Baseline Models (Rosenberg,
> Michael I)
> 6. Re: Automatic Generation of Baseline Models (Paul Riemer)
> 7. Re: Automatic Generation of Baseline Models (Nathan Kegel)
> 8. Re: Automatic Generation of Baseline Models (Sami, Vikram)
> 9. Re: Automatic Generation of Baseline Models (Rosenberg,
> Michael I)
> 10. Re: Automatic Generation of Baseline Models (Eric Oliver)
> 11. Re: Automatic Generation of Baseline Models (Max Tillberg)
> 12. Re: Automatic Generation of Baseline Models
> (Dru.Crawley at bentley.com <mailto:Dru.Crawley at bentley.com>)
>
>
> ----------------------------------------------------------------------
>
> Message: 1
> Date: Thu, 7 Feb 2013 16:35:27 +0000
> From: Christoph Reinhart <tito_ at MIT.EDU <mailto:tito_ at MIT.EDU>>
> To: "bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>"
> <bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: [Bldg-sim] Penetration of energy modeling in new construction
> Message-ID:
>
> <1B23446CBF250648A2FC775DE3FE7E800FDFFA2B at OC11expo28.exchange.mit.edu
> <mailto:1B23446CBF250648A2FC775DE3FE7E800FDFFA2B at OC11expo28.exchange.mit.edu>>
> Content-Type: text/plain; charset="us-ascii"
>
> Dear colleagues,
>
> I vaguely recall past discussions on this forum as to the
> penetration rate on building energy modeling in new construction
> (and retrofit?). Would some of you have relevant numbers for the
> US and other countries to share.
>
> Best,
>
> Christoph
> Christoph Reinhart
> Associate Professor
> Department of Architecture
> Massachusetts Institute of Technology
> 77 Massachusetts Ave, Rm 5-418, Cambridge, MA 02139, USA
> t: 617 253 7714 <tel:617%20253%207714>, f: 617 253 6152
> <tel:617%20253%206152>, creinhart at mit.edu
> <mailto:creinhart at mit.edu><mailto:creinhart at mit.edu
> <mailto:creinhart at mit.edu>>
> Sustainable Design Lab<http://mit.edu/SustainableDesignLab/> |
> DIVA<http://www.diva-for-rhino.com/> | Daysim<http://daysim.com/>
> | mapdwell<http://mapdwell.org/>
>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/9e9bd661/attachment.html>
>
> ------------------------------
>
> Message: 2
> Date: Thu, 7 Feb 2013 09:04:59 -0800
> From: "Rosenberg, Michael I" <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>
> To: "bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>"
> <bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: [Bldg-sim] Automatic Generation of Baseline Models
> Message-ID:
>
> <BE950B042CB6574CA6D34A6DD899EEA29F5EF076CF at EMAIL06.pnl.gov
> <mailto:BE950B042CB6574CA6D34A6DD899EEA29F5EF076CF at EMAIL06.pnl.gov>>
> Content-Type: text/plain; charset="us-ascii"
>
> I am hoping the building simulation community can help answer a
> question for me. What software packages out there automatically
> generate baseline models for the ASHRAE 90.1 Energy Cost Budget
> Methodology or Appendix G? Thanks.
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960 <tel:%28541%29%20844-1960>
> michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnl.gov
> <mailto:michael.rosenberg at pnl.gov>>
> www.pnnl.gov <http://www.pnnl.gov><http://www.pnl.gov/>
>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/0cdb2b3c/attachment-0001.htm>
>
> ------------------------------
>
> Message: 3
> Date: Thu, 7 Feb 2013 09:07:16 -0800
> From: Jeremiah Crossett <jcrossett at phasechange.com
> <mailto:jcrossett at phasechange.com>>
> To: "Rosenberg, Michael I" <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>
> Cc: "bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>"
> <bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
> Message-ID:
>
> <CAPsP_xS_aH4naay=kb1-F=RGRZ+ptbuUKWnV02MWcJUM1RhtZw at mail.gmail.com <mailto:RGRZ%2BptbuUKWnV02MWcJUM1RhtZw at mail.gmail.com>>
> Content-Type: text/plain; charset="iso-8859-1"
>
> Bentley havacomp AECOSIM does for one..
> *
> *
> *
> *
> *Jeremiah D. Crossett | Senior Analyst | Phase Change Energy
> Solutions*
> *
> 120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951
> <tel:503-688-8951>
> www.phasechange.com <http://www.phasechange.com>
> *
>
> *
> *
> *
> *
>
>
>
> On Thu, Feb 7, 2013 at 9:04 AM, Rosenberg, Michael I <
> michael.rosenberg at pnnl.gov <mailto:michael.rosenberg at pnnl.gov>> wrote:
>
> > I am hoping the building simulation community can help answer a
> question
> > for me. What software packages out there automatically generate
> baseline
> > models for the ASHRAE 90.1 Energy Cost Budget Methodology or
> Appendix G?
> > Thanks. ****
> >
> > ** **
> >
> > *__________________________*
> >
> > * *
> >
> > *Michael Rosenberg, CEM, LEED AP *****
> >
> > Senior Research Scientist****
> >
> > ENERGY & ENVIRONMENT DIRECTORATE ****
> >
> > ** **
> >
> > Pacific Northwest National Laboratory ****
> >
> > 2032 Todd Street ****
> >
> > Eugene, OR 97405 ****
> >
> > (541) 844-1960 <tel:%28541%29%20844-1960> ****
> >
> > michael.rosenberg at pnnl.gov <mailto:michael.rosenberg at pnnl.gov>
> <michael.rosenberg at pnl.gov <mailto:michael.rosenberg at pnl.gov>> ****
> >
> > www.pnnl.gov <http://www.pnnl.gov> <http://www.pnl.gov/>****
> >
> > ** **
> >
> > ** **
> >
> > _______________________________________________
> > Bldg-sim mailing list
> > http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> > To unsubscribe from this mailing list send a blank message to
> > BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
> >
> >
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/09575a78/attachment-0001.htm>
>
> ------------------------------
>
> Message: 4
> Date: Thu, 7 Feb 2013 11:13:27 -0600
> From: Jim Dirkes <jim at buildingperformanceteam.com
> <mailto:jim at buildingperformanceteam.com>>
> To: Jeremiah Crossett <jcrossett at phasechange.com
> <mailto:jcrossett at phasechange.com>>, "Rosenberg, Michael
> I" <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>
> Cc: "bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>"
> <bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
> Message-ID:
>
> <FC1586506FC3D647A8CEAB83BA211A6902DEA4F7 at CH2MBX01.ch2.comcast.net
> <mailto:FC1586506FC3D647A8CEAB83BA211A6902DEA4F7 at CH2MBX01.ch2.comcast.net>>
> Content-Type: text/plain; charset="us-ascii"
>
> I think you need to define "automatically" carefully.
> DesignBuilder does a fair amount of the work and Simergy intends
> to do something similar.
> As an example, the proper ASHRAE 90.1 EER / COP is not known until
> you actually run the simulation and find out the capacity. It
> seems to me that some of the criteria must be ascertained from a
> successful simulation before you can have a complete Baseline.
> Another example that has been discussed in this forum is
> calculating the proper fan and pump pressure rise to comply with 90.1
>
> James V Dirkes II, PE, BEMP, LEED AP
> www.buildingperformanceteam.com
> <http://www.buildingperformanceteam.com><http://www.buildingperformanceteam.com/>
> Energy Analysis, Commissioning & Training Services
> 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> 616 450 8653 <tel:616%20450%208653>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>
> [mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of
> Jeremiah Crossett
> Sent: Thursday, February 07, 2013 12:07 PM
> To: Rosenberg, Michael I
> Cc: bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
>
> Bentley havacomp AECOSIM does for one..
>
>
> Jeremiah D. Crossett | Senior Analyst | Phase Change Energy
> Solutions
> 120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951
> <tel:503-688-8951>
> www.phasechange.com
> <http://www.phasechange.com><http://www.phasechange.com>
> [http://i.imgur.com/Sldxf.jpg]
>
>
>
>
> On Thu, Feb 7, 2013 at 9:04 AM, Rosenberg, Michael I
> <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>> wrote:
> I am hoping the building simulation community can help answer a
> question for me. What software packages out there automatically
> generate baseline models for the ASHRAE 90.1 Energy Cost Budget
> Methodology or Appendix G? Thanks.
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960 <tel:%28541%29%20844-1960><tel:%28541%29%20844-1960>
> michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnl.gov
> <mailto:michael.rosenberg at pnl.gov>>
> www.pnnl.gov <http://www.pnnl.gov><http://www.pnl.gov/>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG><mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/a6af9f98/attachment-0001.htm>
>
> ------------------------------
>
> Message: 5
> Date: Thu, 7 Feb 2013 09:19:49 -0800
> From: "Rosenberg, Michael I" <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>
> To: Jim Dirkes <jim at buildingperformanceteam.com
> <mailto:jim at buildingperformanceteam.com>>, Jeremiah Crossett
> <jcrossett at phasechange.com <mailto:jcrossett at phasechange.com>>
> Cc: "bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>"
> <bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
> Message-ID:
>
> <BE950B042CB6574CA6D34A6DD899EEA29F5EF076DE at EMAIL06.pnl.gov
> <mailto:BE950B042CB6574CA6D34A6DD899EEA29F5EF076DE at EMAIL06.pnl.gov>>
> Content-Type: text/plain; charset="us-ascii"
>
> That is a good point Jim. To actually generate a baseline
> following either of the protocols, it is necessary to first do a
> sizing run. So the automation would need to be a two-step process.
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960 <tel:%28541%29%20844-1960>
> michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnl.gov
> <mailto:michael.rosenberg at pnl.gov>>
> www.pnnl.gov <http://www.pnnl.gov><http://www.pnl.gov/>
>
>
> From: Jim Dirkes [mailto:jim at buildingperformanceteam.com
> <mailto:jim at buildingperformanceteam.com>]
> Sent: Thursday, February 07, 2013 9:13 AM
> To: Jeremiah Crossett; Rosenberg, Michael I
> Cc: bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>
> Subject: RE: [Bldg-sim] Automatic Generation of Baseline Models
>
> I think you need to define "automatically" carefully.
> DesignBuilder does a fair amount of the work and Simergy intends
> to do something similar.
> As an example, the proper ASHRAE 90.1 EER / COP is not known until
> you actually run the simulation and find out the capacity. It
> seems to me that some of the criteria must be ascertained from a
> successful simulation before you can have a complete Baseline.
> Another example that has been discussed in this forum is
> calculating the proper fan and pump pressure rise to comply with 90.1
>
> James V Dirkes II, PE, BEMP, LEED AP
> www.buildingperformanceteam.com
> <http://www.buildingperformanceteam.com><http://www.buildingperformanceteam.com/>
> Energy Analysis, Commissioning & Training Services
> 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> 616 450 8653 <tel:616%20450%208653>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org><mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>>
> [mailto:bldg-sim-bounces at lists.onebuildingorg
> <mailto:bldg-sim-bounces at lists.onebuildingorg>] On Behalf Of
> Jeremiah Crossett
> Sent: Thursday, February 07, 2013 12:07 PM
> To: Rosenberg, Michael I
> Cc: bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org><mailto:bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
>
> Bentley havacomp AECOSIM does for one..
>
>
> Jeremiah D. Crossett | Senior Analyst | Phase Change Energy
> Solutions
> 120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951
> <tel:503-688-8951>
> www.phasechange.com
> <http://www.phasechange.com><http://www.phasechange.com>
> [http://i.imgur.com/Sldxf.jpg]
>
>
>
>
> On Thu, Feb 7, 2013 at 9:04 AM, Rosenberg, Michael I
> <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>> wrote:
> I am hoping the building simulation community can help answer a
> question for me. What software packages out there automatically
> generate baseline models for the ASHRAE 90.1 Energy Cost Budget
> Methodology or Appendix G? Thanks.
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960 <tel:%28541%29%20844-1960><tel:%28541%29%20844-1960>
> michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnl.gov
> <mailto:michael.rosenberg at pnl.gov>>
> www.pnnl.gov <http://www.pnnl.gov><http://www.pnl.gov/>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG><mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/a0ab0863/attachment-0001.htm>
>
> ------------------------------
>
> Message: 6
> Date: Thu, 7 Feb 2013 11:37:19 -0600
> From: Paul Riemer <Paul.Riemer at dunhameng.com
> <mailto:Paul.Riemer at dunhameng.com>>
> To: "'Rosenberg, Michael I'" <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>, Jim Dirkes
> <jim at buildingperformanceteam.com
> <mailto:jim at buildingperformanceteam.com>>, Jeremiah Crossett
> <jcrossett at phasechange.com <mailto:jcrossett at phasechange.com>>
> Cc: "bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>"
> <bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
> Message-ID:
> <057EF46662FE994F8119F0A903BCD0F8019CC622AE97 at eml1.dunham.corp>
> Content-Type: text/plain; charset="us-ascii"
>
> If you have waterside systems it really becomes three steps:
>
> 1) Run with all guesses to determine airside sizing
>
> 2) Run with determined airside sizing and guessed waterside
> sizing
>
> 3) Run with known airside and waterside sizing
>
> Then the complications of the rotations and satisfying unmet hours
> criteria.
> If you view modeling like a video game with level to achieve and
> get a good soundtrack, then you can be happily oblivious about how
> much time you are spending on it.
>
> Paul Riemer, PE, LEED AP BD+C
> DUNHAM
>
> From: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>
> [mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of
> Rosenberg, Michael I
> Sent: Thursday, February 07, 2013 11:20 AM
> To: Jim Dirkes; Jeremiah Crossett
> Cc: bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
>
> That is a good point Jim. To actually generate a baseline
> following either of the protocols, it is necessary to first do a
> sizing run. So the automation would need to be a two-step process.
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960
> michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnl.gov
> <mailto:michael.rosenberg at pnl.gov>>
> www.pnnl.gov <http://www.pnnl.gov><http://www.pnl.gov/>
>
>
> From: Jim Dirkes [mailto:jim at buildingperformanceteam.com
> <mailto:jim at buildingperformanceteam.com>]
> Sent: Thursday, February 07, 2013 9:13 AM
> To: Jeremiah Crossett; Rosenberg, Michael I
> Cc: bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>
> Subject: RE: [Bldg-sim] Automatic Generation of Baseline Models
>
> I think you need to define "automatically" carefully.
> DesignBuilder does a fair amount of the work and Simergy intends
> to do something similar.
> As an example, the proper ASHRAE 90.1 EER / COP is not known until
> you actually run the simulation and find out the capacity. It
> seems to me that some of the criteria must be ascertained from a
> successful simulation before you can have a complete Baseline.
> Another example that has been discussed in this forum is
> calculating the proper fan and pump pressure rise to comply with 90.1
>
> James V Dirkes II, PE, BEMP, LEED AP
> www.buildingperformanceteam.com
> <http://www.buildingperformanceteam.com><http://www.buildingperformanceteam.com/>
> Energy Analysis, Commissioning & Training Services
> 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> 616 450 8653
>
> From: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org><mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>>
> [mailto:bldg-sim-bounces at lists.onebuildingorg
> <mailto:bldg-sim-bounces at lists.onebuildingorg>] On Behalf Of
> Jeremiah Crossett
> Sent: Thursday, February 07, 2013 12:07 PM
> To: Rosenberg, Michael I
> Cc: bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org><mailto:bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
>
> Bentley havacomp AECOSIM does for one..
>
>
> Jeremiah D. Crossett | Senior Analyst | Phase Change Energy
> Solutions
> 120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951
> www.phasechange.com
> <http://www.phasechange.com><http://www.phasechange.com>
> [http://i.imgur.com/Sldxf.jpg]
>
>
>
>
> On Thu, Feb 7, 2013 at 9:04 AM, Rosenberg, Michael I
> <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>> wrote:
> I am hoping the building simulation community can help answer a
> question for me. What software packages out there automatically
> generate baseline models for the ASHRAE 90.1 Energy Cost Budget
> Methodology or Appendix G? Thanks.
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960<tel:%28541%29%20844-1960>
> michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnl.gov
> <mailto:michael.rosenberg at pnl.gov>>
> www.pnnl.gov <http://www.pnnl.gov><http://www.pnl.gov/>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG><mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/82c9aab3/attachment-0001.htm>
>
> ------------------------------
>
> Message: 7
> Date: Thu, 7 Feb 2013 17:53:54 +0000
> From: Nathan Kegel <nathan.kegel at iesve.com
> <mailto:nathan.kegel at iesve.com>>
> To: "Rosenberg, Michael I" <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>,
> "bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>"
> <bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
> Message-ID:
>
> <8F29443B220B3D48A035EFB2FEEB8CB430F4DF at GL-EXC-01.iesve.com
> <mailto:8F29443B220B3D48A035EFB2FEEB8CB430F4DF at GL-EXC-01.iesve.com>>
> Content-Type: text/plain; charset="us-ascii"
>
> You do need to be careful about "automatic" - it's a complex thing
> to fully automate. There are more exceptions than rules.
>
> IES VE has a PRM Navigator which automates baselines for both
> 90.1-2004 and 2007 following the PRM methodology (Appendix G).
>
> The PRM Navigator does auto-generate much of the baseline - but
> also allows the user to go in and see and "break" or edit the
> baseline as needed for different conditions.
>
> [Description: IES]<http://www.iesve.com/>
>
> Nathan Kegel
> Project Manager
> Business Development Manager
> Minneapolis
>
> T:
>
> 763 276 9981
>
> M:
>
> 415 420 9314
>
> http://www.iesve.com<http://www.iesve.com/>
>
>
> **Design, Simulate + Innovate with the <Virtual Environment>**
>
> Integrated Environmental Solutions Limited. Registered in Scotland
> No. SC151456
> Registered Office - Helix Building, West Of Scotland Science Park,
> Glasgow G20 0SP
>
> Email Disclaimer<http://www.iesve.com/disclaimer.html>
>
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>
> [mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of
> Rosenberg, Michael I
> Sent: Thursday, February 07, 2013 11:05 AM
> To: bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>
> Subject: [Bldg-sim] Automatic Generation of Baseline Models
>
> I am hoping the building simulation community can help answer a
> question for me. What software packages out there automatically
> generate baseline models for the ASHRAE 90.1 Energy Cost Budget
> Methodology or Appendix G? Thanks.
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960
> michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnl.gov
> <mailto:michael.rosenberg at pnl.gov>>
> www.pnnl.gov <http://www.pnnl.gov><http://www.pnl.gov/>
>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/362925b0/attachment-0001.htm>
> -------------- next part --------------
> A non-text attachment was scrubbed...
> Name: image001.jpg
> Type: image/jpeg
> Size: 2684 bytes
> Desc: image001.jpg
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/362925b0/attachment-0001.jpg>
>
> ------------------------------
>
> Message: 8
> Date: Thu, 7 Feb 2013 12:06:24 -0600
> From: "Sami, Vikram" <Vikram.Sami at perkinswill.com
> <mailto:Vikram.Sami at perkinswill.com>>
> To: Nathan Kegel <nathan.kegel at iesve.com
> <mailto:nathan.kegel at iesve.com>>, "Rosenberg, Michael I"
> <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>,
> "bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>"
> <bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
> Message-ID:
>
> <BF1FB99E0691894F9DCB992DF4DFDE9FEA2B6ECD at chi01exmb.perkinswill.net <mailto:BF1FB99E0691894F9DCB992DF4DFDE9FEA2B6ECD at chi01exmb.perkinswill.net>>
> Content-Type: text/plain; charset="us-ascii"
>
> Echoing everyone's caution for "Automatic" - I think it also
> depends on what you are using it for. If it's for a detailed
> compliance modeling, then I would really caution against it. If
> it's for quick EEM explorations I am sure it's a simpler matter.
>
>
> Vikram Sami, LEED AP BD+C
> Sustainable Design Analyst
> 1315 Peachtree St. NE, Atlanta, GA 30309
> t: 404-443-7462 f: 404.892.5823 e:
> vikram.sami at perkinswill.com <mailto:vikram.sami at perkinswill.com>
> www.perkinswill.com
> <http://www.perkinswill.com><http://www.perkinswill.com/>
> Perkins+Will. Ideas + buildings that honor the broader goals of
> society
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>
> [mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of
> Nathan Kegel
> Sent: Thursday, February 07, 2013 12:54 PM
> To: Rosenberg, Michael I; bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
>
> You do need to be careful about "automatic" - it's a complex thing
> to fully automate. There are more exceptions than rules.
>
> IES VE has a PRM Navigator which automates baselines for both
> 90.1-2004 and 2007 following the PRM methodology (Appendix G).
>
> The PRM Navigator does auto-generate much of the baseline - but
> also allows the user to go in and see and "break" or edit the
> baseline as needed for different conditions.
>
> [cid:image001.jpg at 01CE0533.EE510080]<http://www.iesve.com/>
>
> Nathan Kegel
> Project Manager
> Business Development Manager
> Minneapolis
>
> T:
>
> 763 276 9981
>
> M:
>
> 415 420 9314
>
> http://www.iesve.com<http://www.iesve.com/>
>
>
> **Design, Simulate + Innovate with the <Virtual Environment>**
>
> Integrated Environmental Solutions Limited. Registered in Scotland
> No. SC151456
> Registered Office - Helix Building, West Of Scotland Science Park,
> Glasgow G20 0SP
>
> Email Disclaimer<http://www.iesve.com/disclaimer.html>
>
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>
> [mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of
> Rosenberg, Michael I
> Sent: Thursday, February 07, 2013 11:05 AM
> To: bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>
> Subject: [Bldg-sim] Automatic Generation of Baseline Models
>
> I am hoping the building simulation community can help answer a
> question for me. What software packages out there automatically
> generate baseline models for the ASHRAE 90.1 Energy Cost Budget
> Methodology or Appendix G? Thanks.
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960
> michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnl.gov
> <mailto:michael.rosenberg at pnl.gov>>
> www.pnnl.gov <http://www.pnnl.gov><http://www.pnl.gov/>
>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/fdf31ae8/attachment-0001.htm>
> -------------- next part --------------
> A non-text attachment was scrubbed...
> Name: image001.jpg
> Type: image/jpeg
> Size: 2684 bytes
> Desc: image001.jpg
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/fdf31ae8/attachment-0001.jpg>
>
> ------------------------------
>
> Message: 9
> Date: Thu, 7 Feb 2013 10:12:37 -0800
> From: "Rosenberg, Michael I" <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>
> To: "Sami, Vikram" <Vikram.Sami at perkinswill.com
> <mailto:Vikram.Sami at perkinswill.com>>, Nathan Kegel
> <nathan.kegel at iesve.com <mailto:nathan.kegel at iesve.com>>,
> "bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>"
> <bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
> Message-ID:
>
> <BE950B042CB6574CA6D34A6DD899EEA29F5EF07712 at EMAIL06.pnl.gov
> <mailto:BE950B042CB6574CA6D34A6DD899EEA29F5EF07712 at EMAIL06.pnl.gov>>
> Content-Type: text/plain; charset="us-ascii"
>
> What I was really interested in is software that does the whole
> process automatically. No manipulation on the part of the user at
> all. You input a proposed building design, and following one of
> the rulesets results are generated. Does that exist and if it
> does, for which protocols?
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960
> michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnl.gov
> <mailto:michael.rosenberg at pnl.gov>>
> www.pnnl.gov <http://www.pnnl.gov><http://www.pnl.gov/>
>
>
> From: Sami, Vikram [mailto:Vikram.Sami at perkinswill.com
> <mailto:Vikram.Sami at perkinswill.com>]
> Sent: Thursday, February 07, 2013 10:06 AM
> To: Nathan Kegel; Rosenberg, Michael I;
> bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org>
> Subject: RE: Automatic Generation of Baseline Models
>
> Echoing everyone's caution for "Automatic" - I think it also
> depends on what you are using it for. If it's for a detailed
> compliance modeling, then I would really caution against it. If
> it's for quick EEM explorations I am sure it's a simpler matter.
>
>
> Vikram Sami, LEED AP BD+C
> Sustainable Design Analyst
> 1315 Peachtree St. NE, Atlanta, GA 30309
> t: 404-443-7462 f: 404.892.5823 e:
> vikram.sami at perkinswill.com
> <mailto:vikram.sami at perkinswill.com><mailto:vikram.sami at perkinswill.com
> <mailto:vikram.sami at perkinswill.com>> www.perkinswill.com
> <http://www.perkinswill.com><http://www.perkinswill.com/>
> Perkins+Will. Ideas + buildings that honor the broader goals of
> society
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org><mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>>
> [mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of
> Nathan Kegel
> Sent: Thursday, February 07, 2013 12:54 PM
> To: Rosenberg, Michael I; bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org><mailto:bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
>
> You do need to be careful about "automatic" - it's a complex thing
> to fully automate. There are more exceptions than rules.
>
> IES VE has a PRM Navigator which automates baselines for both
> 90.1-2004 and 2007 following the PRM methodology (Appendix G).
>
> The PRM Navigator does auto-generate much of the baseline - but
> also allows the user to go in and see and "break" or edit the
> baseline as needed for different conditions.
>
> [cid:image001.jpg at 01CE051B.A79C0940]<http://www.iesve.com/>
>
> Nathan Kegel
> Project Manager
> Business Development Manager
> Minneapolis
>
> T:
>
> 763 276 9981
>
> M:
>
> 415 420 9314
>
> http://www.iesve.com<http://www.iesve.com/>
>
>
> **Design, Simulate + Innovate with the <Virtual Environment>**
>
> Integrated Environmental Solutions Limited. Registered in Scotland
> No. SC151456
> Registered Office - Helix Building, West Of Scotland Science Park,
> Glasgow G20 0SP
>
> Email Disclaimer<http://www.iesvecom/disclaimer.html>
>
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org><mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>>
> [mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of
> Rosenberg, Michael I
> Sent: Thursday, February 07, 2013 11:05 AM
> To: bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org><mailto:bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: [Bldg-sim] Automatic Generation of Baseline Models
>
> I am hoping the building simulation community can help answer a
> question for me. What software packages out there automatically
> generate baseline models for the ASHRAE 90.1 Energy Cost Budget
> Methodology or Appendix G? Thanks.
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960
> michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnl.gov
> <mailto:michael.rosenberg at pnl.gov>>
> www.pnnl.gov <http://www.pnnl.gov><http://www.pnl.gov/>
>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/13eb6d2d/attachment-0001.htm>
> -------------- next part --------------
> A non-text attachment was scrubbed...
> Name: image001.jpg
> Type: image/jpeg
> Size: 2684 bytes
> Desc: image001.jpg
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/13eb6d2d/attachment-0001.jpg>
>
> ------------------------------
>
> Message: 10
> Date: Thu, 7 Feb 2013 18:16:43 +0000
> From: Eric Oliver <emo at emoenergy.com <mailto:emo at emoenergy.com>>
> To: "Rosenberg, Michael I" <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>
> Cc: "bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>"
> <bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
> Message-ID: <8E52DFA3-D411-46B0-8156-BE49D7CBF2A2 at emoenergy.com
> <mailto:8E52DFA3-D411-46B0-8156-BE49D7CBF2A2 at emoenergy.com>>
> Content-Type: text/plain; charset="windows-1252"
>
> As far as I'm aware, nothing like that exists. Nor could it,
> ASHRAE 90.1 is too complex to make something like that make every
> decision automated.
>
> Sent from my iPhone
>
> On Feb 7, 2013, at 1:12 PM, "Rosenberg, Michael I"
> <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>> wrote:
>
> What I was really interested in is software that does the whole
> process automatically. No manipulation on the part of the user at
> all. You input a proposed building design, and following one of
> the rulesets results are generated. Does that exist and if it
> does, for which protocols?
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960
> michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnl.gov
> <mailto:michael.rosenberg at pnl.gov>>
> www.pnnl.gov <http://www.pnnl.gov><http://www.pnl.gov/>
>
>
> From: Sami, Vikram [mailto:Vikram.Sami at perkinswill.com
> <mailto:Vikram.Sami at perkinswill.com>]
> Sent: Thursday, February 07, 2013 10:06 AM
> To: Nathan Kegel; Rosenberg, Michael I;
> bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org><mailto:bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: RE: Automatic Generation of Baseline Models
>
> Echoing everyone?s caution for ?Automatic? ? I think it also
> depends on what you are using it for. If it?s for a detailed
> compliance modeling, then I would really caution against it. If
> it?s for quick EEM explorations I am sure it?s a simpler matter.
>
>
> Vikram Sami, LEED AP BD+C
> Sustainable Design Analyst
> 1315 Peachtree St. NE, Atlanta, GA 30309
> t: 404-443-7462 f: 404.892.5823 e:
> vikram.sami at perkinswill.com
> <mailto:vikram.sami at perkinswill.com><mailto:vikram.sami at perkinswill.com
> <mailto:vikram.sami at perkinswill.com>> www.perkinswill.com
> <http://www.perkinswill.com><http://www.perkinswill.com/>
> Perkins+Will. Ideas + buildings that honor the broader goals of
> society
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org><mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>>
> [mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of
> Nathan Kegel
> Sent: Thursday, February 07, 2013 12:54 PM
> To: Rosenberg, Michael I; bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org><mailto:bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
>
> You do need to be careful about ?automatic? ? it?s a complex thing
> to fully automate. There are more exceptions than rules.
>
> IES VE has a PRM Navigator which automates baselines for both
> 90.1-2004 and 2007 following the PRM methodology (Appendix G).
>
> The PRM Navigator does auto-generate much of the baseline ? but
> also allows the user to go in and see and ?break? or edit the
> baseline as needed for different conditions.
>
> <image001.jpg><http://www.iesve.com/>
>
> Nathan Kegel
> Project Manager
> Business Development Manager
> Minneapolis
>
> T:
>
> 763 276 9981
>
> M:
>
> 415 420 9314
>
> http://www.iesve.com<http://www.iesve.com/>
>
>
> **Design, Simulate + Innovate with the <Virtual Environment>**
>
> Integrated Environmental Solutions Limited. Registered in Scotland
> No. SC151456
> Registered Office - Helix Building, West Of Scotland Science Park,
> Glasgow G20 0SP
>
> Email Disclaimer<http://www.iesvecom/disclaimer.html>
>
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org><mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>>
> [mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of
> Rosenberg, Michael I
> Sent: Thursday, February 07, 2013 11:05 AM
> To: bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org><mailto:bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: [Bldg-sim] Automatic Generation of Baseline Models
>
> I am hoping the building simulation community can help answer a
> question for me. What software packages out there automatically
> generate baseline models for the ASHRAE 90.1 Energy Cost Budget
> Methodology or Appendix G? Thanks.
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960
> michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnl.gov
> <mailto:michael.rosenberg at pnl.gov>>
> www.pnnl.gov <http://www.pnnl.gov><http://www.pnl.gov/>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG><mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/1e4f72e4/attachment-0001.htm>
> -------------- next part --------------
> A non-text attachment was scrubbed...
> Name: image001.jpg
> Type: image/jpeg
> Size: 2684 bytes
> Desc: image001.jpg
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/1e4f72e4/attachment-0001.jpg>
>
> ------------------------------
>
> Message: 11
> Date: Thu, 7 Feb 2013 19:22:17 +0100
> From: Max Tillberg <max.tillberg at bengtdahlgren.se
> <mailto:max.tillberg at bengtdahlgren.se>>
> To: "bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>"@bdab.nu <http://bdab.nu>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
> Message-ID:
>
> <OFE3297C1D.8BCA2FB1-ONC1257B0B.00648305-C1257B0B.0064ED1B at bdab.nu
> <mailto:OFE3297C1D.8BCA2FB1-ONC1257B0B.00648305-C1257B0B.0064ED1B at bdab.nu>>
> Content-Type: text/plain; charset="utf-8"
>
> I would say that the LEED plugin for IDA ICE 4.5 does a pretty
> good job.
> For most buildings you need very little manupilation.
>
>
> Sincerely
>
> Max Tillberg
>
> Direkt tel: 031-720 26 12
> E-post: max.tillberg at bengtdahlgren.se
> <mailto:max.tillberg at bengtdahlgren.se>
>
> Bengt Dahlgren G?teborg AB
> Kroksl?tts Fabriker 52, 431 37 M?LNDAL
> Tel: 031-720 25 00
> www.bengtdahlgren.se <http://www.bengtdahlgren.se>
>
> Ingenj?rskonst, helt enkelt
>
>
>
>
> From: Eric Oliver <emo at emoenergy.com <mailto:emo at emoenergy.com>>
> To: "Rosenberg, Michael I" <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>,
> Cc: "bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>"
> <bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Date: 2013-02-07 19:16
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
> Sent by: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>
>
>
>
> As far as I'm aware, nothing like that exists. Nor could it,
> ASHRAE 90.1
> is too complex to make something like that make every decision
> automated.
>
> Sent from my iPhone
>
> On Feb 7, 2013, at 1:12 PM, "Rosenberg, Michael I" <
> michael.rosenberg at pnnl.gov <mailto:michael.rosenberg at pnnl.gov>> wrote:
>
> What I was really interested in is software that does the whole
> process
> automatically. No manipulation on the part of the user at all. You
> input a
> proposed building design, and following one of the rulesets
> results are
> generated. Does that exist and if it does, for which protocols?
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960
> michael.rosenberg at pnnl.gov <mailto:michael.rosenberg at pnnl.gov>
> www.pnnl.gov <http://www.pnnl.gov>
>
>
> From: Sami, Vikram [mailto:Vikram.Sami at perkinswill.com
> <mailto:Vikram.Sami at perkinswill.com>]
> Sent: Thursday, February 07, 2013 10:06 AM
> To: Nathan Kegel; Rosenberg, Michael I;
> bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org>
> Subject: RE: Automatic Generation of Baseline Models
>
> Echoing everyone?s caution for ?Automatic? ? I think it also
> depends on
> what you are using it for. If it?s for a detailed compliance modeling,
> then I would really caution against it. If it?s for quick EEM
> explorations
> I am sure it?s a simpler matter.
>
>
> Vikram Sami, LEED AP BD+C
> Sustainable Design Analyst
> 1315 Peachtree St. NE, Atlanta, GA 30309
> t: 404-443-7462 f: 404.892.5823 e:
> vikram.sami at perkinswill.com <mailto:vikram.sami at perkinswill.com>
> www.perkinswill.com <http://www.perkinswill.com>
> Perkins+Will. Ideas + buildings that honor the broader goals of
> society
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org> [
> mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of
> Nathan Kegel
> Sent: Thursday, February 07, 2013 12:54 PM
> To: Rosenberg, Michael I; bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
>
> You do need to be careful about ?automatic? ? it?s a complex thing to
> fully automate. There are more exceptions than rules.
>
> IES VE has a PRM Navigator which automates baselines for both
> 90.1-2004
> and 2007 following the PRM methodology (Appendix G).
>
> The PRM Navigator does auto-generate much of the baseline ? but also
> allows the user to go in and see and ?break? or edit the baseline as
> needed for different conditions.
>
>
> <image001.jpg>
> Nathan Kegel
> Project Manager
> Business Development Manager
> Minneapolis
>
>
> T:
> 763 276 9981
> M:
> 415 420 9314
> http://www.iesve.com
>
> **Design, Simulate + Innovate with the <Virtual Environment>**
> Integrated Environmental Solutions Limited. Registered in Scotland No.
> SC151456
> Registered Office - Helix Building, West Of Scotland Science Park,
> Glasgow
> G20 0SP
> Email Disclaimer
>
>
> From: bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org> [
> mailto:bldg-sim-bounces at lists.onebuilding.org
> <mailto:bldg-sim-bounces at lists.onebuilding.org>] On Behalf Of
> Rosenberg,
> Michael I
> Sent: Thursday, February 07, 2013 11:05 AM
> To: bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>
> Subject: [Bldg-sim] Automatic Generation of Baseline Models
>
> I am hoping the building simulation community can help answer a
> question
> for me. What software packages out there automatically generate
> baseline
> models for the ASHRAE 90.1 Energy Cost Budget Methodology or
> Appendix G?
> Thanks.
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960
> michael.rosenberg at pnnl.gov <mailto:michael.rosenberg at pnnl.gov>
> www.pnnl.gov <http://www.pnnl.gov>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/7739b2a2/attachment-0001.htm>
> -------------- next part --------------
> A non-text attachment was scrubbed...
> Name: not available
> Type: image/jpeg
> Size: 2684 bytes
> Desc: not available
> URL:
> <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/7739b2a2/attachment-0001.jpeg>
>
> ------------------------------
>
> Message: 12
> Date: Thu, 7 Feb 2013 20:15:29 +0000
> From: <Dru.Crawley at bentley.com <mailto:Dru.Crawley at bentley.com>>
> To: <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>,
> <bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>>
> Subject: Re: [Bldg-sim] Automatic Generation of Baseline Models
> Message-ID:
> <0ux71qsefpm3pnkrneoadq50.1360268125548 at email.android.com
> <mailto:0ux71qsefpm3pnkrneoadq50.1360268125548 at email.android.com>>
> Content-Type: text/plain; charset="us-ascii"
>
> Bentley's AECOSIM Energy Simulator automatically creates baseline
> and budget buildings for Standard 90.1 2004, 2007, and 2010.
>
>
>
>
> -------- Original message --------
> From: "Rosenberg, Michael I" <michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov>>
> Date:
> To: bldg-sim at lists.onebuilding.org
> <mailto:bldg-sim at lists.onebuilding.org>
> Subject: [Bldg-sim] Automatic Generation of Baseline Models
>
>
> I am hoping the building simulation community can help answer a
> question for me. What software packages out there automatically
> generate baseline models for the ASHRAE 90.1 Energy Cost Budget
> Methodology or Appendix G? Thanks.
>
> __________________________
>
> Michael Rosenberg, CEM, LEED AP
> Senior Research Scientist
> ENERGY & ENVIRONMENT DIRECTORATE
>
> Pacific Northwest National Laboratory
> 2032 Todd Street
> Eugene, OR 97405
> (541) 844-1960
> michael.rosenberg at pnnl.gov
> <mailto:michael.rosenberg at pnnl.gov><mailto:michael.rosenberg at pnl.gov
> <mailto:michael.rosenberg at pnl.gov>>
> www.pnnl.gov <http://www.pnnl.gov><http://www.pnl.gov/>
>
>
>
>
> ------------------------------
>
> _______________________________________________
> Bldg-sim mailing list
> Bldg-sim at lists.onebuilding.org <mailto:Bldg-sim at lists.onebuilding.org>
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>
>
> End of Bldg-sim Digest, Vol 63, Issue 5
> ***************************************
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130207/1068a696/attachment-0002.htm>
More information about the Bldg-sim
mailing list