Kevin,
Depending on your system, if you've got high levels of infiltration in a high humidity area, large latent loads within the spaces etc. downstream or room RH could potentially be high. Otherwise, if it's not meeting the off-coil RH, either you've got a profile issue (your coil is effectively off) or some part of your system is undersized. You'll need to interrogate step by step to find the issue.
Taking Chris' point further ApacheHVAC doesn't 'look' at any value from your Room Conditions tab. In that respect it's a dumb beast. It's up to you to make sure the room conditions and setpoint controllers within ApacheHVAC match, so that your loads and your coil/airflow sizing tie up.
Hope that helps,
Ed
Edwin Wealend
Senior Engineer
CUNDALL Hong Kong
9th Floor Chinachem Johnston Plaza
178-186 Johnston Road
Wanchai, Hong Kong
tel: +852 2566 6205
fax: +852 2566 6235
P Please consider the environment before printing this e-mail
Important Notice. Use of this email and any attachments is subject to the terms on www.cundall.com.hk<http://www.cundall.com.hk/>
Please read that notice before proceeding.
If you cannot access these terms please telephone (852) 2566 6260 or reply to this email and we will send you a copy
From: Kevin Campbell [mailto:Kevin.Campbell at megroup.com]
Sent: Friday, February 15, 2013 06:39
To: Chris Yates
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] IES VE Dehumidification Question
I'm using all prototype systems, and they all have humidity controllers attached to the coil/room when imported. Looking at those controllers they have a setpoint of 50% RH with a 10% deadband. I don't know if that's standard with the prototype systems or if it's pulling that from my room conditions tab, but either way everything seems to be pointing to 50% RH.
[Element Logo 4-27-12.png]<http://www.megroup.com/>
KEVIN CAMPBELL, EIT, CxT
ANALYST
t: 402.464.3833 x2129
WE'RE ON OUR JOURNEY TO GREENBUILD 2012!<http://www.megroup.com/index.php/greenbuild2012>
[Signature Twitter]<https://twitter.com/#!/megroup> [Signature LinkedIn Logo] <http://www.linkedin.com/company/m-e-group>
From: Chris Yates [mailto:chris.malcolm.yates at gmail.com]
Sent: Thursday, February 14, 2013 4:21 PM
To: Kevin Campbell
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] IES VE Dehumidification Question
Difficult to diagnose from your description but certain zone level system settings become redundant when you use aphvac.
Are you using the controllers in aphvac to control humidity via coils or are you expecting aphvac to the "find" settings in your zone "room conditions"tab?
It's not always obvious what settings become redundant.
Sent from my Android device. Please excuse typos, etc.
On 14 Feb 2013 14:16, "Kevin Campbell" <Kevin.Campbell at megroup.com><mailto:Kevin.Campbell at megroup.com>> wrote:
Building Simulation Community -
I'm having issues with humidity in some models I'm running while trying to use ApacheHVAC. I have set my "Maximum Percent Saturation" to 50%, and in the VE ASHRAE Loads Results Data tab of the loads data spreadsheet it shows that max input as 50%. If I go into Vista and highlight my "filename.asp" file for the run that is linked to my ApacheHVAC system and run the "Heating and Cooling Report" and look at the "Comfort - Occupied" section all of my rooms have a Max% Relative Humidity of 85-100%. This is the same if I select "Systems" from the drop down and investigate Relative Humidity on a node by node basis at the rooms in my ApacheHVAC system.
Rooms in my model that are not assigned to an ApacheHVAC system and are left with the default ApacheSystems system show that they are being maintained at 50% RH.
All rooms whether assigned to the ApacheHVAC systems or the default systems show that they're letting room temperatures float to Unoccupied setpoints during the "Comfort - Occupied" times.
Any help on this would be greatly appreciated, the buildings I'm trying to work on are located in Louisville, KY and Tampa, FL so not accounting for dehumidification is going to vastly effect the cooling load.
Thanks,
[Element Logo 4-27-12.png]<http://www.megroup.com/>
KEVIN CAMPBELL, EIT, CxT
ANALYST
t: 402.464.3833 x2129<tel:402.464.3833%20x2129>
WE'RE ON OUR JOURNEY TO GREENBUILD 2012!<http://www.megroup.com/index.php/greenbuild2012>
[Signature Twitter]<https://twitter.com/#!/megroup> [Signature LinkedIn Logo] <http://www.linkedin.com/company/m-e-group>
________________________________
CONFIDENTIALITY NOTICE: This e-mail and any attached file(s) are intended only for the use of the individual or entity to whom or to which it is addressed and may contain information that is privileged, confidential, proprietary, and trade secret. If the reader of this message is not the intended recipient or an employee or agent responsible for delivering the message to the intended recipient, you are hereby notified that any dissemination, distribution, or reproduction of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately and discard the original message and any attachment(s).
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
________________________________
CONFIDENTIALITY NOTICE: This e-mail and any attached file(s) are intended only for the use of the individual or entity to whom or to which it is addressed and may contain information that is privileged, confidential, proprietary, and trade secret. If the reader of this message is not the intended recipient or an employee or agent responsible for delivering the message to the intended recipient, you are hereby notified that any dissemination, distribution, or reproduction of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately and discard the original message and any attachment(s).
For further information about Cundall please visit http://www.cundall.com/Locations/Asia/Asia.aspx
--------------------------------------------------------------------------------
Cundall Hong Kong Limited. Registered office: Chinachem Johnston Plaza, 178-186 Johnston Road, Wanchai, Hong Kong.
All information contained in this email is private and confidential, and may also be privileged.
This email and its attachments are intended solely for the use of the addressee only and if any third party whatsoever
comes into possession of this email,they rely on it at their own risk and Cundall accepts no duty or responsibility
(including in negligence) to any such third party.
If you have received this email in error, please immediately notify the sender and delete all copies from your system.
Privacy Policy: Use of this email and any attachments is subject to the terms on our Website at
http://www.cundall.com/Misc/Privacy-Policy.aspx If you cannot access these terms,
please email terms at cundall.com with SEND TERMS in the subject heading or telephone +44 (0191) 213 1515 and we will send you a copy.
All of our business is conducted in accordance with Cundall’s Ethical Business Policy. http://www.cundall.com/Knowledgehub/Ethical-Business-Policy.aspx
--------------------------------------------------------------------------------
This email message has been scanned for viruses by Mimecast. For more information please visit http://www.mimecast.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130218/ded7b996/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 2037 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130218/ded7b996/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 752 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130218/ded7b996/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 784 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130218/ded7b996/attachment-0008.jpg>
More information about the Bldg-sim
mailing list