[Bldg-sim] IES VE Dehumidification Question
Dr Paul Carey
paul at zed-uk.com
Fri Feb 15 08:59:13 PST 2013
Kevin,
Is this not because the room heat loads and cooling loads calculation sheet
pulls results from your .clg and .htg files not your .aps file?
Paul
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Kevin Campbell
Sent: 14 February 2013 22:39
To: Chris Yates
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] IES VE Dehumidification Question
I'm using all prototype systems, and they all have humidity controllers
attached to the coil/room when imported. Looking at those controllers they
have a setpoint of 50% RH with a 10% deadband. I don't know if that's
standard with the prototype systems or if it's pulling that from my room
conditions tab, but either way everything seems to be pointing to 50% RH.
<http://www.megroup.com/> Element Logo 4-27-12.png
KEVIN CAMPBELL, EIT, CxT
ANALYST
t: 402.464.3833 x2129
<http://www.megroup.com/index.php/greenbuild2012> WE'RE ON OUR JOURNEY TO
GREENBUILD 2012!
<https://twitter.com/#!/megroup> Signature Twitter
<http://www.linkedin.com/company/m-e-group> Signature LinkedIn Logo
From: Chris Yates [mailto:chris.malcolm.yates at gmail.com]
Sent: Thursday, February 14, 2013 4:21 PM
To: Kevin Campbell
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] IES VE Dehumidification Question
Difficult to diagnose from your description but certain zone level system
settings become redundant when you use aphvac.
Are you using the controllers in aphvac to control humidity via coils or are
you expecting aphvac to the "find" settings in your zone "room
conditions"tab?
It's not always obvious what settings become redundant.
Sent from my Android device. Please excuse typos, etc.
On 14 Feb 2013 14:16, "Kevin Campbell" <Kevin.Campbell at megroup.com> wrote:
Building Simulation Community -
I'm having issues with humidity in some models I'm running while trying to
use ApacheHVAC. I have set my "Maximum Percent Saturation" to 50%, and in
the VE ASHRAE Loads Results Data tab of the loads data spreadsheet it shows
that max input as 50%. If I go into Vista and highlight my "filename.asp"
file for the run that is linked to my ApacheHVAC system and run the "Heating
and Cooling Report" and look at the "Comfort - Occupied" section all of my
rooms have a Max% Relative Humidity of 85-100%. This is the same if I select
"Systems" from the drop down and investigate Relative Humidity on a node by
node basis at the rooms in my ApacheHVAC system.
Rooms in my model that are not assigned to an ApacheHVAC system and are left
with the default ApacheSystems system show that they are being maintained at
50% RH.
All rooms whether assigned to the ApacheHVAC systems or the default systems
show that they're letting room temperatures float to Unoccupied setpoints
during the "Comfort - Occupied" times.
Any help on this would be greatly appreciated, the buildings I'm trying to
work on are located in Louisville, KY and Tampa, FL so not accounting for
dehumidification is going to vastly effect the cooling load.
Thanks,
<http://www.megroup.com/> Element Logo 4-27-12.png
KEVIN CAMPBELL, EIT, CxT
ANALYST
t: 402.464.3833 x2129 <tel:402.464.3833%20x2129>
<http://www.megroup.com/index.php/greenbuild2012> WE'RE ON OUR JOURNEY TO
GREENBUILD 2012!
<https://twitter.com/#!/megroup> Signature Twitter
<http://www.linkedin.com/company/m-e-group> Signature LinkedIn Logo
_____
CONFIDENTIALITY NOTICE: This e-mail and any attached file(s) are intended
only for the use of the individual or entity to whom or to which it is
addressed and may contain information that is privileged, confidential,
proprietary, and trade secret. If the reader of this message is not the
intended recipient or an employee or agent responsible for delivering the
message to the intended recipient, you are hereby notified that any
dissemination, distribution, or reproduction of this communication is
strictly prohibited. If you have received this communication in error,
please notify us immediately and discard the original message and any
attachment(s).
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
_____
CONFIDENTIALITY NOTICE: This e-mail and any attached file(s) are intended
only for the use of the individual or entity to whom or to which it is
addressed and may contain information that is privileged, confidential,
proprietary, and trade secret. If the reader of this message is not the
intended recipient or an employee or agent responsible for delivering the
message to the intended recipient, you are hereby notified that any
dissemination, distribution, or reproduction of this communication is
strictly prohibited. If you have received this communication in error,
please notify us immediately and discard the original message and any
attachment(s).
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130215/66d0814a/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2037 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130215/66d0814a/attachment-0006.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 752 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130215/66d0814a/attachment-0007.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 784 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130215/66d0814a/attachment-0008.jpeg>
More information about the Bldg-sim
mailing list