To read it another way, COMcheck literally does generate compliance reports which document proposed and allowable LPD’s in an itemized fashion. I answered previously assuming Christian is asking specifically about whether the reports themselves are considered acceptable documentation for LPD tallies/calcs.
Such reports, while intended to document prescriptive code compliance, can serve double-duty as effective LEED model documentation for derived LPD inputs (and other credits). Since LEED EAc1 modeling requires documenting both the baseline and proposed model LPD’s (which correspond to the prescribed allowable and installed watts, respectively), I’ve found COMcheck compliance reports to be quite a timesaver over the self-made spreadsheets I used to assemble.
The .cck files incidentally, by nature of their common structure, are also easier to pass around with other designers to pick up and work with, relative to a “roll your own documentation” approach.
Regards,
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Larry Degelman
Sent: Monday, February 18, 2013 10:05 AM
To: Christian Stalberg; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] COMcheck & bldg sim programs
Christian,
Your question is a bit puzzling, since COMcheck doesn’t literally “report” LPDs. It reveals the allowable LPDs based on the energy code specified by the user at input time; but it’s the responsibility of the user to input the actual (proposed) LPDs by either the whole-building method or the space-by-space method. COMcheck only tells you whether you’re exceeding the code limitation you specified.
I would think that you could always rely on the soundness of the “allowable” LPDs shown in COMcheck, since they are reflecting the code requirements. However, and energy simulation model inputs always need to be the LPDs that are actually in the building design.
Regards,
Larry
===============================
Larry O. Degelman, P.E., BEMP, HBDP
Professor Emeritus of Architecture
Texas A&M University
===============================
From: Christian Stalberg<mailto:cstalberg at naturalintelligence.us>
Sent: Monday, February 18, 2013 8:24 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] COMcheck & bldg sim programs
Can anyone tell me if the LPD as reported by COMcheck is a sound input for whole building energy performance simulation programs? If not, why not?
Thank you in advance!
---
Christian Stalberg
Principal
Natural Intelligence, LLC
http://naturalintelligence.us <blocked::blocked::http://naturalintelligence.us/>
Tel. 919.986.9237
________________________________
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
________________________________
No virus found in this message.
Checked by AVG - www.avg.com<http://www.avg.com>
Version: 2013.0.2897 / Virus Database: 2639/6110 - Release Date: 02/17/13
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130218/7071a303/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130218/7071a303/attachment-0002.jpg>
More information about the Bldg-sim
mailing list