[Bldg-sim] Fan Power
Aaron Smith
asmith at mreng.ca
Fri Feb 22 17:53:06 PST 2013
Small FHP HVAC motors can have efficiencies below 50% which is why ECM motors are becomming popular in that size range - they are typically 65-85% efficient. See in the presentation below where w/cfm is 1/3 with ECM vs PSC.
http://www.energy.ca.gov/title24/2013standards/prerulemaking/documents/2011-08-17_workshop/presentations/08%2520EC%2520Motors.pdf
Aaron
Aaron Smith, P.Eng
M&R Engineering Ltd.
Sent on the TELUS Mobility network with BlackBerry
-----Original Message-----
From: Jim Dirkes <jim at buildingperformanceteam.com>
Date: Fri, 22 Feb 2013 19:11:43
To: RobertWichert<robert at wichert.org>; Aaron Smith<asmith at mreng.ca>
Cc: bldg-sim at lists.onebuilding.org<bldg-sim at lists.onebuilding.org>; Scott Blunk<scott at buildingscientist.com>
Subject: RE: [Bldg-sim] Fan Power
Based on Aaron’s calculations, it sounds like 44% = motor efficiency x fan efficiency, That’s the net which affects energy use – how it is composed doesn’t matter too much.
Small motors often have terrible efficiency. The same is true for small fans! Put them together and it’s pretty dismal.
James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com<http://www.buildingperformanceteam.com/>
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of RobertWichert
Sent: Friday, February 22, 2013 8:07 PM
To: Aaron Smith
Cc: bldg-sim at lists.onebuilding.org; Scott Blunk
Subject: Re: [Bldg-sim] Fan Power
A 50% efficient MOTOR cannot be correct. 50% efficient fan, yes.
I actually think a lot of the amps given are something akin to MCA.
Let's see what others say...
Robert P. Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
On Feb 22, 2013, at 1:51 PM, Aaron Smith <asmith at mreng.ca<mailto:asmith at mreng.ca>> wrote:
Robert,
I’ve also run into problems obtaining combined (fan and motor) efficiency and input power, mostly with terminal units such as heat pumps and fan coil units but also with individual fans. What I’ve often done is used the watts listed in their electrical tables. For example, below if you take their size 20 at high fan speed, they classify the motor HP at 1/30HP or 25W (output power). I’ve taken the subsequent columns to mean input power so the watts at 115V is then 57W which would make the motor is 44% efficient and that seems reasonable to me. The listed amps don’t necessarily equate to the same wattages, they are usually higher so my only theory is that this is the starting amps.
I’d be interested in finding out what other have to say. I have tried talking to some local equipment reps without any luck.
Aaron
<image002.jpg>
Aaron Smith, P.Eng
M&R Engineering
-----Original Message-----
From: RobertWichert [mailto:robert at wichert.org]
Sent: Friday, February 22, 2013 12:25 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>; Scott Blunk
Subject: [Bldg-sim] Fan Power
This is a DOE-2 question, I think, but I am applying it to EnergyPro. I
am asking here in the hopes that some will have a more in-depth
knowledge of DOE-2 and how it relates to fan power. I am also hoping
that some here will be able to reflect on the theory and application of
fan power and energy as it relates to actual systems and modeling.
When inputting indoor fan power, I have used many sources for the fan
power. I sometimes use the motor nameplate, which I believe is too high
in every case.
I also sometimes use FLA or RLA, which I also do not believe are
accurate, but sometimes give more realistic numbers.
Some manufacturers give fan BHP at design conditions, which I find to be
very helpful, but not everybody is that helpful.
It has been suggested that I calculate the fan BHP using the theoretical
formula *** Fan BHP = (cfm x static press "w.c.) / (6356 x fan
efficiency) *** and then use a conservative fan efficiency (maybe 50%)
for a good number. This gives a much lower value than the other
methods, and I am trying to see if there is anything wrong with this
approach.
As I understand the usage, indoor fan power is divided by motor and
drive efficiency to come up with fan energy. So the fan BHP is the
starting point. Having this too high drives up fan energy, sometimes
dramatically, and can influence the proposed case quite a bit if there
are lots of fans, even small fans.
Any thoughts on this approach would be very much appreciated.
--
Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130223/1fbe8692/attachment-0002.htm>
More information about the Bldg-sim
mailing list