[Bldg-sim] Fan Power
Graham Carter & Megan Lyall
hamnmegs at ozemail.com.au
Fri Feb 22 18:54:26 PST 2013
The data is very hard to come by, but 44% for the motor only I believe is about right in those smaller motors. 35% wouldn't surprise me with maybe a 60-65% direct drive blower so 20% wire-air wouldn't be out of the ballpark in my opinion. The motors are historically single phase split capacitor historically and a poorer quality than a small 3 phase induction motor.
On a tangent, 3 phase induction motor efficiencies really drop off below 1.5 HP or so. Unless of a very high quality / HE then the part load efficiency can also be very poor despite the full load efficiency looking OK. So a small 3 phase motor could have 85% full load / full speed efficiency but at 25% load (say 50% speed and 50% torque) the efficiency can be dramatically poorer. We have managed to get part load motor efficiency data from TECO and others in the past that go down to 50% torque but at full speed (thus 50% load) so not that helpful as variable speed / variable pressure systems spend time at much lower loads. The data does typically show a peak efficiency at 75% load however where I2R losses have dropped but eddy current and other losses haven't started to dominate the losses and thus drive efficiency down which they do at lower loads.
We have a large project where we have asked contractors and thus suppliers to test select equipment on their test rigs to generate better part load data. We will see how we go.
Fortunately with a lot of smaller equipment digital motors or electrically commutated motors have lifted efficiencies dramatically as they are direct drive and being digital the variable speed controls are intrinsic to the motor.
Getting part load efficiencies out of VSD drive suppliers we have found to be like drawing blood out of a stone. I assume that there is a large fixed component of losses so at part load in % terms the VSD losses could grow from 3% say to 7-10%. Don't forget your belts as well if you are taking a fan manufacturer's bhp figures as they typically do not include the belts - maybe 3-5% in losses if well aligned and tensioned.
If you have variable flow, variable pressure systems that spend a lot of time at very low loads, the VSD can affect the motor efficiency at lower loads. There was an ASHRAE Transactions paper or RP from the late 90's I recall that showed motor part load efficiency without a VSD drive and then with and there was a difference. If I remember correctly they did the test with a SE motor but may have also done with a HE motor and the HE motors are more resilient to the impacts of a VSD.
I guess all I am trying to say is that getting a full load design point is one thing, but make sure it includes all the losses and more importantly make sure you take a view on what happens at part load as that is where larger modern systems operate. Smaller systems may be constant flow / constant speed but increasingly we are seeing variable speed FCUs etc available on the market using ECMs.
Regards,
Graham
On 23/02/2013, at 12:11 PM, Jim Dirkes wrote:
> Based on Aaron’s calculations, it sounds like 44% = motor efficiency x fan efficiency, That’s the net which affects energy use – how it is composed doesn’t matter too much.
> Small motors often have terrible efficiency. The same is true for small fans! Put them together and it’s pretty dismal.
>
> James V Dirkes II, PE, BEMP, LEED AP
> www.buildingperformanceteam.com
> Energy Analysis, Commissioning & Training Services
> 1631 Acacia Drive, Grand Rapids, MI 49504 USA
> 616 450 8653
>
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of RobertWichert
> Sent: Friday, February 22, 2013 8:07 PM
> To: Aaron Smith
> Cc: bldg-sim at lists.onebuilding.org; Scott Blunk
> Subject: Re: [Bldg-sim] Fan Power
>
> A 50% efficient MOTOR cannot be correct. 50% efficient fan, yes.
>
> I actually think a lot of the amps given are something akin to MCA.
>
> Let's see what others say...
>
>
>
> Robert P. Wichert P.Eng. LEED AP BD&C
> +1 916 966 9060
> FAX +1 916 966 9068
>
> On Feb 22, 2013, at 1:51 PM, Aaron Smith <asmith at mreng.ca> wrote:
>
> Robert,
>
> I’ve also run into problems obtaining combined (fan and motor) efficiency and input power, mostly with terminal units such as heat pumps and fan coil units but also with individual fans. What I’ve often done is used the watts listed in their electrical tables. For example, below if you take their size 20 at high fan speed, they classify the motor HP at 1/30HP or 25W (output power). I’ve taken the subsequent columns to mean input power so the watts at 115V is then 57W which would make the motor is 44% efficient and that seems reasonable to me. The listed amps don’t necessarily equate to the same wattages, they are usually higher so my only theory is that this is the starting amps.
>
> I’d be interested in finding out what other have to say. I have tried talking to some local equipment reps without any luck.
>
> Aaron
>
> <image002.jpg>
>
>
> Aaron Smith, P.Eng
> M&R Engineering
>
> -----Original Message-----
> From: RobertWichert [mailto:robert at wichert.org]
> Sent: Friday, February 22, 2013 12:25 PM
> To: bldg-sim at lists.onebuilding.org; Scott Blunk
> Subject: [Bldg-sim] Fan Power
>
> This is a DOE-2 question, I think, but I am applying it to EnergyPro. I
> am asking here in the hopes that some will have a more in-depth
> knowledge of DOE-2 and how it relates to fan power. I am also hoping
> that some here will be able to reflect on the theory and application of
> fan power and energy as it relates to actual systems and modeling.
>
> When inputting indoor fan power, I have used many sources for the fan
> power. I sometimes use the motor nameplate, which I believe is too high
> in every case.
>
> I also sometimes use FLA or RLA, which I also do not believe are
> accurate, but sometimes give more realistic numbers.
>
> Some manufacturers give fan BHP at design conditions, which I find to be
> very helpful, but not everybody is that helpful.
>
> It has been suggested that I calculate the fan BHP using the theoretical
> formula *** Fan BHP = (cfm x static press "w.c.) / (6356 x fan
> efficiency) *** and then use a conservative fan efficiency (maybe 50%)
> for a good number. This gives a much lower value than the other
> methods, and I am trying to see if there is anything wrong with this
> approach.
>
> As I understand the usage, indoor fan power is divided by motor and
> drive efficiency to come up with fan energy. So the fan BHP is the
> starting point. Having this too high drives up fan energy, sometimes
> dramatically, and can influence the proposed case quite a bit if there
> are lots of fans, even small fans.
>
>
> Any thoughts on this approach would be very much appreciated.
>
>
>
> --
> Robert Wichert P.Eng. LEED AP BD&C
> +1 916 966 9060
> FAX +1 916 966 9068
>
>
>
>
>
>
>
> ===============================================
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130223/6bcfbe03/attachment-0002.htm>
More information about the Bldg-sim
mailing list