[Bldg-sim] Fan Power
RobertWichert
robert at wichert.org
Sun Feb 24 19:02:56 PST 2013
Well, OK, I will bow to your expertise, but a 44% motor sounds pretty
dismal to me, as you suggest.
Would a conservative number be 20%, air to wire? Is so, I am looking
for FAN efficiency. NOT motor or drive efficiency, which are taken care
of by the modeling software separately.
Would 50% for FAN efficiency by reasonable?
If so, this allows me to use the theoretical air BHP equation to
calculate fan BHP at design conditions using 50% fan efficiency. This
would be a big breakthrough for me, actually.
I do like the idea of actual testing, which is rare as hen's teeth.
Even amp numbers are way too high. I have had RLA that show more HP
than the nominal motor HP. That's gotta be wrong.
I have not seen a single ECM fan coil unit with an improved fan BHP.
Not one. If you got one, please share your knowledge!
Cheers from sunny California.
Robert Wichert P.Eng. LEED AP BD&C
+1 916 966 9060
FAX +1 916 966 9068
===============================================
On 2/22/2013 6:54 PM, Graham Carter & Megan Lyall wrote:
> The data is very hard to come by, but 44% for the motor only I believe
> is about right in those smaller motors. 35% wouldn't surprise me with
> maybe a 60-65% direct drive blower so 20% wire-air wouldn't be out of
> the ballpark in my opinion. The motors are historically single phase
> split capacitor historically and a poorer quality than a small 3 phase
> induction motor.
>
> On a tangent, 3 phase induction motor efficiencies really drop off
> below 1.5 HP or so. Unless of a very high quality / HE then the part
> load efficiency can also be very poor despite the full load efficiency
> looking OK. So a small 3 phase motor could have 85% full load / full
> speed efficiency but at 25% load (say 50% speed and 50% torque) the
> efficiency can be dramatically poorer. We have managed to get part
> load motor efficiency data from TECO and others in the past that go
> down to 50% torque but at full speed (thus 50% load) so not that
> helpful as variable speed / variable pressure systems spend time at
> much lower loads. The data does typically show a peak efficiency at
> 75% load however where I2R losses have dropped but eddy current and
> other losses haven't started to dominate the losses and thus drive
> efficiency down which they do at lower loads.
>
> We have a large project where we have asked contractors and thus
> suppliers to test select equipment on their test rigs to generate
> better part load data. We will see how we go.
>
> Fortunately with a lot of smaller equipment digital motors or
> electrically commutated motors have lifted efficiencies dramatically
> as they are direct drive and being digital the variable speed controls
> are intrinsic to the motor.
>
> Getting part load efficiencies out of VSD drive suppliers we have
> found to be like drawing blood out of a stone. I assume that there is
> a large fixed component of losses so at part load in % terms the VSD
> losses could grow from 3% say to 7-10%. Don't forget your belts as
> well if you are taking a fan manufacturer's bhp figures as they
> typically do not include the belts - maybe 3-5% in losses if well
> aligned and tensioned.
>
> If you have variable flow, variable pressure systems that spend a lot
> of time at very low loads, the VSD can affect the motor efficiency at
> lower loads. There was an ASHRAE Transactions paper or RP from the
> late 90's I recall that showed motor part load efficiency without a
> VSD drive and then with and there was a difference. If I remember
> correctly they did the test with a SE motor but may have also done
> with a HE motor and the HE motors are more resilient to the impacts of
> a VSD.
>
> I guess all I am trying to say is that getting a full load design
> point is one thing, but make sure it includes all the losses and more
> importantly make sure you take a view on what happens at part load as
> that is where larger modern systems operate. Smaller systems may be
> constant flow / constant speed but increasingly we are seeing variable
> speed FCUs etc available on the market using ECMs.
>
> Regards,
> Graham
>
> On 23/02/2013, at 12:11 PM, Jim Dirkes wrote:
>
>> Based on Aaron's calculations, it sounds like 44% = motor efficiency
>> x fan efficiency, That's the net which affects energy use -- how it
>> is composed doesn't matter too much.
>> Small motors often have terrible efficiency. The same is true for
>> small fans! Put them together and it's pretty dismal.
>> *James V Dirkes II, PE, BEMP, LEED AP**
>> **www.buildingperformanceteam.com*
>> <http://www.buildingperformanceteam.com/>*
>> **Energy Analysis, Commissioning & Training Services**
>> *1631 Acacia Drive, Grand Rapids, MI 49504USA
>> 616 450 8653
>> *From:*bldg-sim-bounces at lists.onebuilding.org
>> <mailto:bldg-sim-bounces at lists.onebuilding.org>[mailto:bldg-sim-bounces at lists.onebuilding.org]*On
>> Behalf Of*RobertWichert
>> *Sent:*Friday, February 22, 2013 8:07 PM
>> *To:*Aaron Smith
>> *Cc:*bldg-sim at lists.onebuilding.org
>> <mailto:bldg-sim at lists.onebuilding.org>; Scott Blunk
>> *Subject:*Re: [Bldg-sim] Fan Power
>> A 50% efficient MOTOR cannot be correct. 50% efficient fan, yes.
>> I actually think a lot of the amps given are something akin to MCA.
>> Let's see what others say...
>>
>>
>> Robert P. Wichert P.Eng. LEED AP BD&C
>> +1 916 966 9060
>> FAX +1 916 966 9068
>>
>>
>> On Feb 22, 2013, at 1:51 PM, Aaron Smith <asmith at mreng.ca
>> <mailto:asmith at mreng.ca>> wrote:
>>
>> Robert,
>> I've also run into problems obtaining combined (fan and motor)
>> efficiency and input power, mostly with terminal units such as
>> heat pumps and fan coil units but also with individual fans.
>> What I've often done is used the watts listed in their electrical
>> tables. For example, below if you take their size 20 at high fan
>> speed, they classify the motor HP at 1/30HP or 25W (output
>> power). I've taken the subsequent columns to mean input power so
>> the watts at 115V is then 57W which would make the motor is 44%
>> efficient and that seems reasonable to me. The listed amps don't
>> necessarily equate to the same wattages, they are usually higher
>> so my only theory is that this is the starting amps.
>> I'd be interested in finding out what other have to say. I have
>> tried talking to some local equipment reps without any luck.
>> Aaron
>> <image002.jpg>
>> Aaron Smith, P.Eng
>> M&R Engineering
>> -----Original Message-----
>> From: RobertWichert [mailto:robert at wichert.org]
>> Sent: Friday, February 22, 2013 12:25 PM
>> To:bldg-sim at lists.onebuilding.org
>> <mailto:bldg-sim at lists.onebuilding.org>; Scott Blunk
>> Subject: [Bldg-sim] Fan Power
>> This is a DOE-2 question, I think, but I am applying it to
>> EnergyPro. I
>> am asking here in the hopes that some will have a more in-depth
>> knowledge of DOE-2 and how it relates to fan power. I am also hoping
>> that some here will be able to reflect on the theory and
>> application of
>> fan power and energy as it relates to actual systems and modeling.
>> When inputting indoor fan power, I have used many sources for the fan
>> power. I sometimes use the motor nameplate, which I believe is
>> too high
>> in every case.
>> I also sometimes use FLA or RLA, which I also do not believe are
>> accurate, but sometimes give more realistic numbers.
>> Some manufacturers give fan BHP at design conditions, which I
>> find to be
>> very helpful, but not everybody is that helpful.
>> It has been suggested that I calculate the fan BHP using the
>> theoretical
>> formula *** Fan BHP = (cfm x static press "w.c.) / (6356 x fan
>> efficiency) *** and then use a conservative fan efficiency (maybe
>> 50%)
>> for a good number. This gives a much lower value than the other
>> methods, and I am trying to see if there is anything wrong with this
>> approach.
>> As I understand the usage, indoor fan power is divided by motor and
>> drive efficiency to come up with fan energy. So the fan BHP is the
>> starting point. Having this too high drives up fan energy, sometimes
>> dramatically, and can influence the proposed case quite a bit if
>> there
>> are lots of fans, even small fans.
>> Any thoughts on this approach would be very much appreciated.
>> --
>> Robert Wichert P.Eng. LEED AP BD&C
>> +1 916 966 9060
>> FAX +1 916 966 9068
>> ===============================================
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send a blank message
>> toBLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>> <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130224/cb916c18/attachment-0001.htm>
More information about the Bldg-sim
mailing list