[Bldg-sim] Really need some deep DOE-2 theology on this one..
Karen Walkerman
karen at secondlaw.biz
Sat Sep 28 18:53:08 PDT 2013
If the "roofs" don't have a zone as the outside boundary condition, then
the model views them as roofs exposed to the exterior. You need to fix
this. If the spaces on the other side have the same thermostat setpoints,
then the easiest thing to do is set the roof type to "adiabatic". This will
save you from having to define new polygons if the floor above has
different zone shapes. For a roof that is only partially covered by the
floor above, you need to create the new polygons. Sorry.
--
Karen
On Sep 28, 2013 9:41 PM, "Patrick J. O'Leary, Jr." <poleary1969 at gmail.com>
wrote:
> this sounds like you have multiple shells in one model for this to
> occur? i'm pretty sure equest views an exterior wall/roof as an exterior
> wall/roof even if it is bounded by an interior wall. i had this problem
> come up on one of my own models where i ended up having a building wing
> meet the building trunk & as i had put them in as 2 separate shells equest
> did not recognize the dividing wall where the wing met the trunk as being
> an interior wall & assigned it (via the wizard) an exterior wall
> definition. i didn't catch this until reviewing the unmet load hour ss-r &
> s-va reports & couldn't figure out why the load was so high. changed the
> definition of the wall to interior (with a door) in detailed mode and the
> unmet load hours went to zero and the load came down.
>
> my understanding (in my case) is that if you create multiple shells and
> place them with a common wall that you want to be an interior the shell
> rotations need to be zero, even if you have the separation between the two
> shells occur at a 45 deg angle (then ask mr. architect about that one).
>
> On 9/28/13 4:47 PM, John Aulbach wrote:
>
> Hi Gang:
>
> I need to elite for this one, and you know who you are..
>
> I am reviewing another party's eQuest model submitted for LEED. The
> reviewer noted that the roof area far exceeded the actual building
> footprint.
>
> Well, guess why? Somehow, the other party made several floors ROOFS
> instead of ceilings. I might be able to simply turn the exterior spaces
> into interior ceilings, but one roof (over an unheated underground garage)
> is partially uder the building and partially exposed to the
> "sidewalk/entrance" of the building.
>
> The BIG Kahuena is this..if a space is crammed next to an adjacent space
> and one of the spaces claims an Exterioir surface between them, does DOE-2
> think that Exterior surface is seeing outdoor conditions? Or does it ignore
> such a thin and merely considers the heat transfer between the spaces (like
> the wall/roof is NOT exposed to the outdoors)?
>
> My approach is this (unless you disagree)..leave the Exterior wall/roof
> along and explain that the model (now in Detailed Edit form) would need
> major surgery to correct to show actual roof area. Having the "roofs" there
> versus floors will not change the thermodynamics of heat transfer.
>
> I yield to the floor.
>
> John Aulbach, PE
>
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130928/933ce302/attachment-0002.htm>
More information about the Bldg-sim
mailing list