You might find the report by morrison hershfield useful for researching
methodologies.
<http://www.morrisonhershfield.com/ashrae1365research/Pages/Insights-Publica
tions.aspx>
http://www.morrisonhershfield.com/ashrae1365research/Pages/Insights-Publicat
ions.aspx
Jeremiah D. Crossett | Senior Analyst | Phase Change Energy Solutions
120 E. Pritchard St. | Asheboro, NC 27203 | Mobile 503-688-8951
www.phasechange.com <http://www.phasechange.com>
<http://i.imgur.com/Sldxf.jpg>
On Mon, Sep 30, 2013 at 9:04 AM, Nathan Miller <nathanm at rushingco.com
<mailto:nathanm at rushingco.com> > wrote:
It isn't like the reviewer is making things up, I think it is pretty clear
from the language of 90.1 Appendix G that you have to account for these
exposed slab edges. Frankly 90.1-2007 is a little more forgiving, allowing
for area-weighted U-factors for the entire wall, I believe previous versions
of Appendix G (2004 for example) actually specifically required that you
model uninsulated assemblies as their own discrete wall types. See excerpts
below:
ASHARE 90.1-2007 Appendix G:
ASHRAE 90.1-2004 Appendix G:
We usually model the slab edges as separate walls (only about 1 foot high)
and make the other walls "shorter" when you take out this area. If you don't
do this in the wizard, you can set up a macro in the .inp to to it, but it
takes a bit of work. Frankly if you already have the model set up without
slab areas, it seems much easier to to do the weighted U-factor calculation.
Nathan Miller - PE, LEEDRAP BD+C, CEM
Mechanical Engineer/Senior Energy Analyst
RUSHING | D 206-788-4577 <tel:206-788-4577> | O 206-285-7100
<tel:206-285-7100>
Our new web site: <http://www.rushingco.com/> www.rushingco.com
From: bldg-sim-bounces at lists.onebuilding.org
<mailto:bldg-sim-bounces at lists.onebuilding.org>
[mailto:bldg-sim-bounces at lists.onebuilding.org
<mailto:bldg-sim-bounces at lists.onebuilding.org> ] On Behalf Of Sherif Farag
Sent: Sunday, September 29, 2013 9:32 AM
To: bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Above Grade External Wall Area Weighted U-value
Calculation
Dear All,
I have submitted a project for review and received a comment requesting me
to include the concrete slabs between floors (Not drop beams) in the
External Wall' area weighted U-value calculation, the reviewer believes that
concrete slabs acts as a thermal bridge and should be insulated from the
outer side (The slab thickness), my understanding that concrete slab
shouldn't be regarded as a part of the occupied area and therefore shouldn't
be included in the area weighted U-value calculation.
I would appreciate if you can advise on the above query!
Thanks & Best Regards,
Sherif Farag
Senior Sustainability Consultant
P.O. Box: 127842
Abu Dhabi, UAE
M: +971 55 199 0022 <tel:%2B971%2055%20199%200022> | E:
sherif.sabr at gmail.com <mailto:sherif.sabr at gmail.com> | Skype ID:
sherif.farag9
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
<mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130930/d4daefe4/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 103514 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130930/d4daefe4/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 64314 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20130930/d4daefe4/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list