This matches my experience as well for plug loads.
I would only plan to itemize plug loads for LEED documentation if attempting to document an energy saving measure above and beyond 90.1 pertaining to receptacle loads (such as plug load circuit controls required by the upcoming title 24).
ASHRAE recommends 0.75 W/ft2 for office building receptacle power density in the user's manual for 90.1-2007 (for when you don't have better data to found the inputs on).  10W/m2 is approximately 0.93W/ft2 (if my math is right), so that's certainly within a reasonable range of expectations.
I do not anticipate you will have any issues.  I've regularly documented exactly the value per the user's manual citing that as the source in my documentation with no further comment.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Duggin, Cory
Sent: Thursday, February 13, 2014 3:26 PM
To: David Eldridge; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Leed eac1 Plug loads
I've never had to provide an itemized list for equipment loads after simply telling them the receptacle loads were modeled as designed per space type.
Cory Duggin, EI
Energy Engineer I
TLC Engineering for Architecture
direct:
615-346-1939
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of David Eldridge
Sent: Thursday, February 13, 2014 3:24 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Leed eac1 Plug loads
At lower than 25% levels GBCI likely will ask for an itemized list to show that you've considered all of the potential contributors. In addition to Fred's list, add elevators if these aren't separately modeled. Water coolers. Anything that shows up with a connection in the electrical plans.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: bldg-sim-bounces at lists.onebuilding.org<mailto:bldg-sim-bounces at lists.onebuilding.org> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Fred Betz
Sent: Thursday, February 13, 2014 3:17 PM
To: Chris Yates; bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] Leed eac1 Plug loads
Chris,
The plug loads are the plug loads. The 25% is just a guidance value from USGBC/GBCI. I've been over and under this level numerous times without a problem.
If you've used the load estimated by the mechanical and/or electrical engineers and apply an appropriate schedule then it should be good enough.
When you're under the 25% threshold a text box will appear for you to explain why. Just state that you've modeled the plug loads as designed.
10 W/m2 sounds a little low for an office. If the owner has made a commitment to use Energy Star devices or laptops for everyone, then 10 W/m2 is plausible. Don't forget to include other equipment like servers/IT equipment, copiers and kitchen equipment (microwave, coffee maker, etc.)
Fred
Fred Betz  PhD., LEED AP (r)BD&C
Senior Sustainable
Systems Analyst
AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI  53719
P: 608.236.1175 | F: 608.238.2614
fbetz at aeieng.com<mailto:fbetz at aeieng.com>  |  www.aeieng.com<http://www.aeieng.com/>
From: Chris Yates [mailto:chris.malcolm.yates at gmail.com]
Sent: Thursday, February 13, 2014 2:28 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] Leed eac1 Plug loads
Dear bldg sim'rs
I'm a little concerned that the plug loads I've modelled in my offices are low and could leed to some unwanted usgbc comments.
I'm meeting the 25% requirement but the peak load in the offices is 10w/m2. Whilst i dont think this is overly optimistic the reviewers may think otherwise. Has anybody had experience of plug loads being queried in detail?
Many thanks
Chris
Sent from my Android device. Please excuse typos, etc.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140213/ba351e27/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140213/ba351e27/attachment-0002.jpg>
    
    
More information about the Bldg-sim
mailing list