[Bldg-sim] 90.1-2007 Exterior Lighting Allowance calculation
    Jones, Christopher 
    cjones at halsall.com
       
    Tue Jul 15 13:11:26 PDT 2014
    
    
  
Alex,
Thanks for the clarification!
Christopher Jones, P.Eng.
Tel: 416.644.4226 * Toll Free: 1.888.425.7255 x 527
From: AChapin at sriregistrar.com [mailto:AChapin at sriregistrar.com]
Sent: Tuesday, July 15, 2014 4:06 PM
To: bldg-sim at lists.onebuilding.org
Cc: Jones, Christopher
Subject: 90.1-2007 Exterior Lighting Allowance calculation
Hi Christopher,
You are only allowed to include the allowance of one or the other surface type (i.e. entrance or canopy/overhangs). You can pick the one that is the most beneficial, but you can't include both.
Alex N. Chapin
Sustainability Program Engineer
SRI Green Building Certification, LLC
300 Northpointe Circle * Suite 304
Seven Fields, PA 16046 * USA
www.SRIRegistrar.com<file:///\\SRI-FS1\WPDOCS\07%20Marketing%20&%20Sales\01Marketing-PARTIAL\01Marketing\Email%20Footer\www.SRIRegistrar.com>
achapin at SRIRegistrar.com<mailto:achapin at SRIRegistrar.com>
T: (724) 934-9000 x619
F: (724) 935-6825
Building Sustainability
This message and any included attachments are from SRI Quality System Registrar, and are intended only for the addressee. The information contained herein may include privileged or confidential information. Unauthorized review, forwarding, printing, copying, distributing or using such information is strictly prohibited and may be unlawful. If you have received this message in error, or have reason to believe that you are not authorized to receive it, please promptly delete it and notify the sender by e-mail with a copy to mail at sriregistrar.com<mailto:mail at sriregistrar.com>.  Thank you.
Date: Tue, 15 Jul 2014 12:40:11 +0000
From: "Jones, Christopher" <cjones at halsall.com<mailto:cjones at halsall.com>>
To: "bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>" <bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>>
Subject: [Bldg-sim] 90.1-2007 Exterior Lighting Allowance calculation
Message-ID: <25F861E695EA99478F9790869A57C7D4DC804C at catormsx02>
Content-Type: text/plain; charset="us-ascii"
Table 9.4.5 includes allowance for Building Entrances and exits (W/linear feet) and Canopies and Overhangs (W/ft2).  If a door has a canopy do you include the allowance for both the W/linear feet and the W/ft2 of canopy?
Thanks for any insights!
Christopher Jones, P.Eng.
Halsall Associates
Tel: 416.644.4226 * Toll Free: 1.888.425.7255 x 527 *  www.halsall.com<http://www.halsall.com/>
Vancouver * Calgary * Sudbury  * Burlington * Toronto * Ottawa
Best Workplaces in Canada, Seven Consecutive Years: 2007 - 2013
___________________________
A Parsons Brinckerhoff Company
______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.
______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20140715/6073bb3e/attachment.htm>
    
    
More information about the Bldg-sim
mailing list