[Bldg-sim] How can Low-e glass have dramatically lower U-Value?
    Blake, Jeff 
    Jeff.Blake at NRCan-RNCan.gc.ca
       
    Wed Jul 30 07:42:02 PDT 2014
    
    
  
Randy,
Some of the commonly used simulation engines do account for the effects of low-e glass on window surfaces (for example, Energy Plus and ESP-r). That is to say that these engines estimate the long wave radiation from interior surfaces (and devices) to the interior surface of the glass and radiated through the various glass panes and interstitial gases to the sky/surroundings.
Low-e coatings effect the overall U-value of windows because of their effect on reflected long wave radiation. Which low-e coating is most appropriate for the North is important since the coatings will affect both the SHGC and the U-value, depending on their type, thickness and the surface they're applied to.
The results of a recent study of a Northern Canadian city (in NWT) concluded that hard coat windows, despite their higher cost and relatively higher U-value make sense in terms of both energy savings and cost-effectiveness.
Jeff Blake, P.Eng.
Sustainable Buildings & Communities | Bâtiments et des collectivités durables
CanmetENERGY | CanmetÉNERGIE
www.canmetENERGY.nrcan.gc.ca
-----Original Message-----
From: Randy Wilkinson [mailto:randallcwilkinson at gmail.com] 
Sent: July 28, 2014 16:35
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] How can Low-e glass have dramatically lower U-Value?
I went into this thinking that the Low-e coating would simply change the SHGC and not change the U-Values much.  I suspected that Low-e coatings would NOT save energy in the far North since they would block the wanted solar heat gain.  Since the manufacturers are claiming a U-value improvement from the Low-e coating, It looks like I can't calculate the savings using our normal energy modeling software. If the U-value improvement they give is in lieu of a more direct calculation method, and is accepted by the community (you all), then I will accept and move on to the next problem.
Thanks to all for your comments.
Randy
On 07/28/2014 12:56 PM, Jones, Christopher wrote:
> Keep in mind that you want a higher SHGC in the north to maximize passive heat gain.
> The framing and glazing spacer selection is important.  Argon fill is a must have.
>
> Christopher Jones, P.Eng.
> Tel: 416.644.4226 * Toll Free: 1.888.425.7255 x 527
>
>
> -----Original Message-----
> From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On 
> Behalf Of Randy Wilkinson
> Sent: Monday, July 28, 2014 2:55 PM
> To: bldg-sim at lists.onebuilding.org
> Subject: [Bldg-sim] How can Low-e glass have dramatically lower U-Value?
>
> Bldg-Simers,
>
> I wanted to see if Low-e glass saves energy in the far North (60 deg. N latitude or more).  My thought was to use the same U-value for the glass, but change the SHGC to account for the difference in solar heat gain due to the Low-e coatings.  To my surprise, manufacturers data for Low-e glass lists much lower U-values for the same double glazed units except with a Low-e coating on surface #3.
>
> I'm having a hard time understanding how a coating a few molecules thick, improves the U-value so much.  The Architects in my firm say that the manufacturers are calculating an improved U-value to account for energy saved by blocking radiant heat lost (going from inside, out) in Winter.  They surmize this is done because our energy loads and modeling software cannot calculate radiant heat loses in Winter.  I'm not sure the weather data we use has hourly long wave radiation data that can be used to determine the available IR heat that can be blocked by the Low-e coating.  I don't think our energy modeling software can account for radiant heat leaving the building in Winter.
>
> For example,
>
> Pilkington 1" double pane clear glass using air, has a Winter U-value 
> of
> 0.47 Btu/hr.sq ft F and an SHGC of 0.71
>
> The same Pilkington unit with their Energy Advantage Low-e coating has 
> a Winter U-value of 0.33  and an SHGC of 0.67
>
> PPG lists similar improvement for their Low-e coating
>
>
> Is our energy modeling software inadequate to accurately model the effects of Low-e coating on glass? Both Summer and Winter?
>
> Can we trust that the glass manufactures are giving us improved U-Values due to Low-e coatings that are valid?
>
> Randy Wilkinson