Sebastian,
In the EE4 Modeling guide under Built-Up VAV, they state that you have the
option to choose between Series VAV Terminal and Parallel VAV Terminal but
that is greyed out in EE4. With that being said I'm not sure what the best
way to model the system is if you stay in EE4 - you would need to account
for the intermittent terminal fan power somehow.
>From what I can tell in the DOE-2 basics guide you should model this type of
system as a Powered Induction Unit (PIU) which doesn't appear to be
available in EE4 so you would need to modify the .doe file in a text editor
and run the simulation outside of EE4. Refer to the attached.
Regards,
Aaron
Aaron Smith, P.Eng
M&R Engineering
-----Original Message-----
From: Carleton Inbox [mailto:juan.carrizo at alumni.carleton.ca]
Sent: Wednesday, March 12, 2014 7:26 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Fan powered VAV in EE4
Hi all,
I'm trying to model a VAV system with parallel fan powers boxes at the zone
level. Is there a workaround to of this in EE4?
Thanks,
Sebastian