[Bldg-sim] 90.1 - Exterior lighting parking
Nicholas Caton
ncaton at catonenergy.com
Fri Aug 7 06:47:41 PDT 2015
To build on Elizabeth’s response:
If the fixtures illuminating what could be classified as “nontradable”
parking are also illuminating tradable surfaces (i.e. uncovered parking),
it is to your advantage for a LEED model to treat all parking areas as
uncovered. GBCI would have you match wattage for those areas between
baseline/proposed cases, and you can’t “double-count” the area between
surface types. The net result is that associated installed power is a
“dead load” on your relative savings potential.
If you are documenting installed lighting power to simply demonstrate
compliance with 90.1-2010 however (outside of a LEED project), such
non-tradable distinctions will generally help your case. I like to avoid
more work than necessary however, and for a large exterior takeoff will
usually run the numbers first without carving out nontradable surface
distinctions. In my experience: unless you have a lot of façade lighting
to account for, compliance can often be demonstrated with only tradable
surface allowances, and you can then just call it a day and move on to the
next thing.
Best of luck!
~Nick
*NICK CATON, P.E.*
*Owner*
*Caton Energy Consulting*
306 N Ferrel
Olathe, KS 66061
office: 785.410.3317
www.catonenergy.com
*From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] *On Behalf
Of *Elizabeth Gillmor
*Sent:* Thursday, August 06, 2015 4:10 PM
*To:* Julien.Dutel at mern.gouv.qc.ca
*Cc:* bldg-sim at lists.onebuilding.org
*Subject:* Re: [Bldg-sim] 90.1 - Exterior lighting parking
My interpretation is that yes, you can add it, but in most cases you
probably don't want to. I would only dip into the non-tradable if you
can't stay under your standard tradable parking allowance, since it would
only hurt your savings otherwise. (Non-tradable must be modeled
identically in baseline/proposed.)
Cheers,
Elizabeth
*Elizabeth Gillmor **PE, LC, LEED AP*
*e n e r g e t i c s **consulting engineers, llc*
energetics-eng.com
c 303.619.0091
2015-08-06 14:57 GMT-06:00 <Julien.Dutel at mern.gouv.qc.ca>:
Hello,
In a project for a 24h retail, the exterior lighting need to comply to
ASHRAE 90.1 2010 (zone 3). I’m focusing on table 9.4.3-B:
· In tradable surfaces, there is “Uncovered Parking areas/Parking
areas and drive = 1.1 W/m2”
· In non-tradable surfaces, there is “Parking near 24-hour retail
entrances = 800 W per Main entry”
My project has a main entry just next a 2000 m2 parking.
Does anyone know if I can add the 800 W to the 2200 W allowed for the
parking (2000 m2 x 1.1 W/m2)?
Many thanks
Julien
*Julien Dutel,* ing., CEM, CMVP*.*
Direction des secteurs résidentiel, institutionnel et des affaires
Bureau de l'efficacité et de l'innovation énergétiques
Ministère des Ressources naturelles
5700, 4e Avenue Ouest, B-406
Québec (Québec) G1H 6R1
Téléphone : 418 627-6379, poste 8060
Téléphone sans frais : 1 877 727-6655
Télécopieur : 418 643-5828
http://www.efficaciteenergetique.mrn.gouv.qc.ca
*AVIS DE CONFIDENTIALITÉ*
*Ce message est confidentiel. Il est à l'usage exclusif du destinataire
ci-dessus. Si vous n'êtes pas le destinataire visé ou une personne
autorisée à lui remettre cette communication, vous êtes par la présente
avisé qu'il est expressément interdit* *de le diffuser, de le distribuer,
de le reproduire,* *d'en dévoiler la teneur ou de prendre quelque mesure
fondée sur l'information qui y est contenue. S’il vous a été envoyé par
erreur, veuillez en informer immédiatement l'expéditeur par téléphone au
418 627-6379 <418%20627-6379> et détruire ce message ainsi que toute copie
de celui-ci.*
*P* Devez-vous vraiment imprimer ce courriel? Si oui, pensez l’imprimer
recto-verso!
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150807/9e51e65c/attachment.htm>
More information about the Bldg-sim
mailing list