[Bldg-sim] ASHRAE 90.1 fan power limitation calculation question
Maria Karpman
maria.karpman at karpmanconsulting.net
Wed Jul 29 15:44:56 PDT 2015
Here is an abstract from 90.1 User’s Manual that answers your question:
Pressure Drop Adjustment Devices
This section provides a description of the
types of devices that quality for additional
fan power. …
………
Return and/or exhaust airflow control devices.
Some types of spaces such as laboratories,
test rooms, or operating rooms require
that an airflow control device be provided
at both the supply air delivery point and at
the exhaust. The exhaust airflow control
device is typically modulated to maintain a
negative or positive space pressure relative
to surrounding spaces. An additional
pressure drop and associated brake
horsepower adjustment is permitted when
this type of device is installed. The credit
may be taken when some spaces served by
an air handler have exhaust airflow devices
and other spaces do not. However, the
credit is taken only for the CFM of air that
is delivered to spaces with a qualifying
exhaust air flow device.
--
Maria Karpman LEED AP, BEMP, CEM
________________
Karpman Consulting
<http://www.karpmanconsulting.net/> www.karpmanconsulting.net
Phone 860.430.1909
41C New London Turnpike
Glastonbury, CT 06033
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher
Sent: Wednesday, July 29, 2015 6:06 PM
To: bldg-sim at onebuilding.org
Subject: [Bldg-sim] ASHRAE 90.1 fan power limitation calculation question
For the baseline fan power limitation, the pressure drop allowances are defined. I am a bit fuzzy on the definition of "Return/Exhaust Control Devices". A system with a return fan and OA economizer typically has dampers to control the flow of the OA, return/exhaust air streams. Would these dampers qualify as a Return/Exhaust Control Device?
cid:image003.png at 01D09C46.E75BA0D0
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0065
www.wspgroup.com <http://www.wspgroup.com/>
_____
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4821 / Virus Database: 4365/10324 - Release Date: 07/28/15
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150729/c79d0ac5/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 6574 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150729/c79d0ac5/attachment.png>
More information about the Bldg-sim
mailing list