[Bldg-sim] ASHRAE 90.1 fan power limitation calculation question
MIke Tillou
michael.tillou at gmail.com
Wed Jul 29 15:58:18 PDT 2015
HI Chris,
The base fan power allowance already includes the necessary pressure drop for return/exhaust dampers in the air handler. The adjustment for exhaust/return control devices refers to damper boxes or other devices used to control space pressurization like you would typically find in a laboratory or hospital.
Cheers,
Michael Tillou, PE, LEED AP BD+C, ASHRAE BEMP
Associate
Atelier Ten
Environmental Design Consultants + Lighting Designers
45 East 20th Street, 4th Floor
New York NY 10003
T +1 (212) 254 4500 x208
F +1 (212) 254 1259
michael.tillou at atelierten.com
www.atelierten.com
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher
Sent: Wednesday, July 29, 2015 6:06 PM
To: bldg-sim at onebuilding.org
Subject: [Bldg-sim] ASHRAE 90.1 fan power limitation calculation question
For the baseline fan power limitation, the pressure drop allowances are defined. I am a bit fuzzy on the definition of "Return/Exhaust Control Devices". A system with a return fan and OA economizer typically has dampers to control the flow of the OA, return/exhaust air streams. Would these dampers qualify as a Return/Exhaust Control Device?
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0065
www.wspgroup.com <http://www.wspgroup.com/>
_____
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com <mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150729/7df9e26d/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 6574 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150729/7df9e26d/attachment.png>
More information about the Bldg-sim
mailing list