[Bldg-sim] Modelling heating
k bk
planetkbk at gmail.com
Wed Mar 25 13:16:23 PDT 2015
1) Make sure your zoning pattern will not require any reheat. Certain VAV
zones served by the same system may require reheat if the central ahu
supplies much cooler air than what is required by some zones.
2) If there is no heating system in your building you should not include it
in the model. Make sure the heating system is set to Not installed. Then
the heating setpoint does not even matter.
>
>
> *From:* Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] *On
> Behalf Of *Rathna Shree
> *Sent:* Wednesday, March 25, 2015 4:59 AM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] Modelling heating
>
>
>
> Dear All,
>
>
>
> In few of the climatic conditions we work on doesn't require heating at
> all. The temperature might go little less than 20deg C in winter but
> heating will definitely not be installed in the project. For these
> projects, how do we set the heating set point temperatures so that heating
> never switches on. we are facing issues especially while modelling VAV with
> PFP boxes in equest (PIU systems). The base case and proposed case heating
> and fan energy consumption are highly affecting the final savings results.
> I am looking to avoid this scenario and ensure heating never switches on,
> therefore zone fans also do not work.
>
>
>
> Please guide.
>
>
>
> Regards,
>
> Rathnashree
>
>
> ------------------------------
> *This message and any attachments contain information intended for a
> specific party and may include sensitive or confidential material. If you
> are not the intended recipient, please do not read, copy, use, or disclose
> to others. Please notify the sender of the delivery error by reply and then
> permanently delete this message and all attachments.*
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150325/64e441e2/attachment.htm>
More information about the Bldg-sim
mailing list