When I had a similar project, we realized early on that the process energy would be so high that savings in other end uses wouldn’t really matter. Basically we needed to get 10% energy cost savings in the manufacturing process energy in order to meet EAp2.
You then must establish a baseline. The USGBC has guidance on this, but if I remember correctly, you have to find 3 similar facilities designed in the last 5 years that use what would be considered the standard practice equipment. You average them for your baseline. I think the details of this are in a CIR.
Cory Duggin, PE, LEED AP BD+C
Associate/Energy Engineer
TLC Engineering for Architecture
direct:
615-346-1939
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of ????
Sent: Thursday, March 26, 2015 4:13 AM
To: Equest-users; bldg-sim
Subject: [Bldg-sim] The solution to manufacturing process load for LEED energy simulation
Dear everyone,
I have found a opinion about the the soultion to manufacturing process load for LEED energy simulation in internet,but I can not confirm if it is correct,does anyone can help me to confirm that or present some different opinions?
The solution is shown as following:
The biggest challenge you will face is in getting reduction for energy savings, as the process energy for your factory also has to be included in the calculation. In some factory projects the process energy itself can go up to 85 - 90% of the total energy. Getting a reduction like 12 - 15% on these might be very challenging. So, first you need to check how much would your process energy for the manufacturing process be.
For your energy model, ASHRAE 90.1 does not suggest a baseline value for the factory process, as every factory process would be very different and unique. So, you will need to create a baseline on your own. You may do this by looking at standard processes and equipments used by other chemical factories, set that as a baseline and try to model energy savings through the equipments and processes your project is using. Check if you propose to use high efficiency equipments. This in the end has to be acceptable by USGBC.
For the energy model, you can consider using a software like IPMVP, which is quite flexible in developing baselines and calculating design case for different types of unique projects. There is also an option for using the default process energy of 25% for your process loads instead of the actual, which might make energy savings more possible.
Bright task lighting and lower overhead lighting can also help in reducing overall energy for the project.
------------------
Yongqing Zhao
Changsha Green Building & Energy Saving Technology CO.,LTD
NO.438,Shaoshan Road,Changsha,Hunan,China
Telephone:13574805636
Email:zhaoyongqing1987 at 126.com
503271081 at qq.com<mailto:503271081 at qq.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20150326/b7f432aa/attachment.htm>
More information about the Bldg-sim
mailing list