[EnergyPlus_Support] Simulation Parameters, Convergence tolerances



What is the load convergence tolerance? Is it a relative value or absolute value? What unit? In Watt or %

What is the temperature convergence tolerance? Is it a relative value or absolute value? What unit? In deg.C or %?

All tolerances have units so the temperature tolerance is in degrees C (or degrees K) and the loads tolerance is in Watts.  Both tolerances work the same way, just one looks at temperatures and one looks at heating and cooling loads.

After the second warmup day, the program compares the maximum temperature experienced in a space with the maximum temperature from the previous day.  If those two temperatures are within the tolerance, then it has passed the first warmup check.

It does a similar comparison with lowest temperatures experience within all the zones.  If the current simulation day and the previous day values are within the tolerance, then it has passed the second warmup check.

Similar things are done with the loads tolerance and the maximum heating and cooling loads that are experienced within the spaces.  Those are compared individually to the values for the previous day.  If they are both in tolerance, then the simulation has passed the third and fourth warmup check.

The simulation stays in the warmup period until ALL FOUR checks have been passed.